default said : " Take no notice of the majority of these as they just seem as though they like to argue rather than knowing what there doing. "

But do you know what you're doing? Because I think what you're suggesting wouldn't be compliant.
Explain why you think this.
 
The post in the beginning was referring to A TNcs in the main property, but TT to the outer building asking what should be.
Exporting a TNcs is fine has long has their is no extraneous metel work in the outer building and if so then a either bond back or TT it
 
@default has the right kind of idea but the wording is a little suspect. Let me adjust it a bit:
To stop this you can install a separate isolator split the tails and used a suitably sized switched fuse at the mains so it doesn't come from the board in the house then run the SWA to the shed from that. Your running a sub main not a finale circuit As the SWA cable has an earthed metal covering it does not need protecting by an RCD for Impact Protection purposes, though may for fault protection.
 
The post in the beginning was referring to A TNcs in the main property, but TT to the outer building asking what should be.
Exporting a TNcs is fine has long has their is no extraneous metel work in the outer building and if so then a either bond back or TT it
You can still export a TNCS to a shed if there is metal work in it. This shed is not a special location.
 
Explain why you think this.
Tim at post #33

Exporting a PME earth isn't as simple as you suggest, as there will be a number of factors that have to be taken into account, depending on its use.
You wouldn't want to be running a 16mm 3 core swa to a customers wooden potting shed that is 2mtrs away, has no extraneous earths and has just one lighting point.

On the other hand, you wouldn't want to export to a cattle shed.




 
Last edited:
Pretty mouth at Post #34

Exporting a PME earth isn't as simple as you suggest, as there will be a number of factors that have to be taken into account, depending on its use.
You wouldn't want to be running a 16mm 3 core swa to a customers wooden potting shed that is 2mtrs away, has no extraneous earths and has just one lighting point.


The original post said nothing about specific factors. So unless it's a metal container, swimming pool, caravan or some other type of special location there are no regs saying it can not be exported.
 
You can still export a TNCS to a shed if there is metal work in it. This shed is not a special location
1668499947968.png

Read this might help.
 
The original post said nothing about specific factors. So unless it's a metal container, swimming pool, caravan or some other type of special location there are no regs saying it can not be exported.
Nobody said any different.
 
It has already been mentioned on here that you are not 'EXPORTING' TN-C-S you are utilising a cpc derived from a TN-C-S earthing system.
 