Dec 8, 2022
3
1
33
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Construction Project Manager
I'm working on a site in the UK where a joinery company will be installing bespoke vanity cabinets.
The cabinets will have MDF/mirrored doors with a demista (heated pad) laminated between the mirror and the MDF door.
The Demista is powered by a 24v SELV transformer, located behind a small panel in the cabinet, in the normal way.

There is a cable, run from the transformer, via a routing, into a tiny pocket behind the Blum hinge mounting plate, in the cabinet side.
The cable is terminated with a spring connector, which is clamped by the Blum hinge mounting plate, see attachment mountingplate.png

There is a corresponding cable and spring connector in the 35mm round drilling for the actual Blum hinge, which would be clamped by the hinge - see attachment hingeplate.png

The 24v power for the demista is intended to flow through the hinge itself - the actual metal body of the Blum hinge will be energised with 24v, from the SELV transformer.
The hinge at the top of the door would be positive and the hinge at the bottom would be negative from the SELV transformer.
The hinges are around 80cm apart.
The door itself will be lacquered MDF.

There is a lot of debate at the moment over the acceptability of using the exposed metal body of the hinge as a conductor.
The on-site electrician doesn't have a problem with it, but I am just slightly uncomfortable.

Does this comply with UK regs?
If it doesn't, please can someone point me in the direction of the regulations it contravenes?

Many thanks in advance!
 

Attachments

  • hingeplate.png
    hingeplate.png
    160.6 KB · Views: 15
  • mountingplate.png
    mountingplate.png
    119.4 KB · Views: 14
Has anyone tested it electrically? Not just with an ohmeter, but using a tester which feeds a current through to test it under stress. Similar to an earth bond test, but obviously this is not being used as an earth.

Any high resistance will create heat and a) waste power and b) possibly be fire risk

Also, what effect will the ingress of damp and moisture make to this joint? Bearing in mind it is only pressure holding the contacts against each other.

Having said that, it's a clever idea.
 
Has anyone tested it electrically? Not just with an ohmeter, but using a tester which feeds a current through to test it under stress. Similar to an earth bond test, but obviously this is not being used as an earth.

Any high resistance will create heat and a) waste power and b) possibly be fire risk

Also, what effect will the ingress of damp and moisture make to this joint? Bearing in mind it is only pressure holding the contacts against each other.

Having said that, it's a clever idea.
I'm assured that the joinery company have done extensive long term testing under load.
I don't have it to hand, but I have seen a table of acceptable pad sizes for this set-up, including the current draw. They also specify the wire size that should be used, and I also recall that they advise against using 12V Demistas because of the increased current that they draw, compared to the same size 24V pads.

I'm not an electrician - I am a curious construction project manager, and certainly not qualified to comment on the overall set-up - hence my post here!

Getting another spark onto site won't be an option for now - this isn't directly my responsibility, and at this stage, it would ruffle far too many feathers, as I am sure you can imagine!


Assuming the joinery company have done appropriate testing, and the hinge isn't introducing high resistance or getting hot, how would this setup sit within the regs?
Something about it just makes me feel slightly uneasy. I'm being told it's fine, but my unease makes me want an informal second opinion.
Are you really allowed to have exposed extra low voltage conductors in zone 2 of a bathroom?
 
  • Like
Reactions: DPG
would this setup sit within the regs?
Something about it just makes me feel slightly uneasy. I'm being told it's fine, but my unease makes me want an informal second opinion.
Are you really allowed to have exposed extra low voltage conductors in zone 2 of a bathroom?

You mention that it is fed from an SELV supply so there won't be a shock risk. I can't see any reason within the regulations why this should be a problem.

I don't like it as a setup, but that's personal opinion and not regulation.
 
  • Agree
Reactions: DPG
You mention that it is fed from an SELV supply so there won't be a shock risk. I can't see any reason within the regulations why this should be a problem.

I don't like it as a setup, but that's personal opinion and not regulation.
Hi Davesparks, thank you for your reply.

A colleague has mentioned 414.4.1 as not being satisfied just now.
I'm not an electrician, but I don't think they are interpreting this correctly.
Could you look at this?

edit to add that there is a 24V LED strip in the same cabinet.
This is an IP rated LED tape, fed from a different SELV transformer.
The tape is housed in an aluminium extrusion, with a plastic diffuser clipped in.

Could this bear relevance to the regulation noted?
 

Attachments

  • 414.4.1.png
    414.4.1.png
    38 KB · Views: 12

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Construction Project Manager

Thread Information

Title
Demista pads powered by a 24v SELV transformer, with cabinet hinge used as a conductor
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
mc_nebula,
Last reply from
mc_nebula,
Replies
4
Views
1,476

Advert