Jul 25, 2023
Bedford
I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs).
6A breaker in Garage consumer panel is tripping on inrush current. House consumer panel 32A breaker for garage is also tripping occasionally. Both are type B. No surprises so far.
Garage consumer panel has old style integrated wylex plug-in breakers (2-way - 32A for sockets & 6A for lighting). Cannot seem to find type-c or type-d plug-in replacements. Does anyone know where to find them - or if they even exist?
Probably need to change house consumer panel breaker to type-c? Am slightly surprised 32A breaker is tripping.
Does anyone know of any in-line delay-on module that can be wired into the lighting so I can stagger the lights on in banks. I can easily divide the lights into 3 banks that come on 1 sec after each other. I’d like to avoid having to switch/wire each bank separately.
Many thanks.
I discovered MeanWell have published their suggested number of power supplies/lights that can be fed with and without their current limiting unit ICL-16. It looks like their unit should do the job. If it were me, I'd give it a try!
PS There is a Wylex 10A breaker for your garage unit, but I don't think there were type C or D of that style. Could be wrong!
Reactions: Pretty Mouth
Thanks a lot for the info.
That device is exactly what I am after - if it limits the current appropriately.
From what I read, it limits inrush current to 16A - which is more than 6, but perhaps short enough duration to make a difference.
Perhaps that and a 10A breaker, might be enough to make it over the line.
Reactions: Avo Mk8
You’ll need to check you can still meet zs requirements for ads when changing from a b type to c type.
Thanks again for all the info.
Do you think this inrush current limiter can be wired directly after the breaker - or do you think it needs to be downstream of the switch?
I don't think it matters. The product spec. shows it wired after the breaker, but that's for their SMPS example.
The quiescent current is given as 1.5W, so putting it after the switch might save a few pennies a year!
Personally I thought the long plastic box form factor version might be easier to accommodate somewhere in the garage, but you could put the DIN version in the CU if there's room.
Awesome. Thanks for the clarification. Makes sense.
I’ll wire it in the garage, on the main feed for all the lights (Inc outdoor floods which are PIR switched LEDs).
That way if everything comes on at once (say, resetting a breaker in CU), it will limit inrush on all transformers - floods, interior lights, cameras, etc.
Reactions: Avo Mk8
Just for fun🤔 I worked out that on the lights main feed it will consume 1.31 kW hours of electricity in a year, so about 40p per annum!!
note to self - must get a life 🤪
Good luck with the installation - I hope that thing works - do let us know the outcome!
Works like a charm!
All lights are connected & no more breaker trips.
The only annoyance is that the inline version doesn’t have provision for earth termination, so have to do that separately, but otherwise, it does exactly what I needed.
Thanks again, very much @Avo Mk8
This has quite a high current rating, but might do the job?
There may be other units around more suitable.
What a great ready-made device!
I have made similar things to keep transformer-input units from burning out relays: an NTC thermistor as inrush suppression and then a zero-crossing SSR to bypass it once established, so it cools for the next cycle...
Works like a charm!
Spoke too soon
Seems that after a number of switches the (10A garage) breaker trips.
Most times, when the lights switch on, the breaker makes a noise (but doesn’t trip). After enough of these, it goes.
I guess I could put a larger breaker. (At some point, probably replace garage CP and put a C-type breaker. )
Spoke too soon
Sorry to hear that 🙁
What's the cable size of the lighting circuit, and is it clipped direct, and are there any other accessories such as junction boxes (eg rated at 10A) on the circuit?
Since the surge device limits current to 16A, just wondering if a 16A type B might be a possible solution? Might have to upgrade the light switch to 20A - MK do one.
Could be scuppered by what the panel MI's say about protection?
Reactions: pc1966
Cable is all 1.5mm^2
Wago boxes are all 20A or 40A. Switches are motion sensing - rated nowhere near 20A.
I will try a 16A breaker to see if that resolves it - at least until I replace the CP.
Otherwise I will need to replace CP now, in order to use a C-type breaker. I was trying to avoid replacing CP right now because I’m sure I will need to make modifications when the inevitable car charging port needs to be installed.
You can't just swap in a C type MCB or even a higher rated one.
You need to confirm that it is safe to do this, including checking that the earth fault loop impedance is low enough to be safe with a different MCB.
If the switches are not suitably rated for these changes they may also need to be replaced.
I suspect that this line from your opening post:
Is at the root of your problems.
With 16A breaker, no more trips.
Will upgrade CP to use a smaller but slower breaker.
Reactions: Avo Mk8
Bedford
Solutions for LED inrush current
Lighting Forum
Greg Hinksman,
Greg Hinksman,