I was under the impression that we were to assume a value of 16ka(but I could be wrong)
That would be with the old BS1361 -3 service fuses...
I was under the impression that we were to assume a value of 16ka(but I could be wrong)
According to the OSG the maximum fault current likely to be found in domestic properties in the UK (unless in heavily built up areas) is 16kA.I was under the impression that we were to assume a value of 16ka(but I could be wrong)
aesmith, can you go and zoom in and get a picture of the plate on the tranny?
Far too tidy!!!Below is an install done by member Dave85. You can't get any clearer than that. Nice job Dave.
![]()

Sadly most of the contributors can no longer share their wit and wisdom with us, which is very sad.This is another nice thread.
Well Dan,on your recommendation ,I decided to read this thread (all 12 pages of it). Very interesting.Feels a lot older than 10 years.It also raised a question for me ,based on the comment above from "Engineer54". He suggests that the metallic sheath of a TNS cable must be electrically isolated as soon as the TNS supply is converted to TNCS.Why does this have to be done?If you have a neutral connected to an installations earth terminal (eg PME/TNC-S) then the incoming supply cables metallic sheath connection must be disconnected. Especially important where a supply cable is suppling both TN-S and TNC-S earthing arrangements!! eg, ....where the DNO cable is in the process of being PME'd....