I think these overhead earthing systems are being done away with due to copper theives leaving the rural customer without an earth


Not a chance in hell, the cost of taking most of these overhead supplies underground will cost more money than what the banks lost, when the massive fraud scam came to light!! lol!!
 
Think you'll find that for most BS88 fuses it's 80KA, not 50KA....
BS88-2 50kA
BS88-6 80kA
BS88-3 33kA
I think, so with just BS88 and no following number a minimum of 50kA, unless it is a BS1361 that is now BS88-3.
 
no I meant the dno just leaving the poor consumer with a TT and having to fend for themselves for a local earth rod(consumers responsibility)
 
I was under the impression that we were to assume a value of 16ka(but I could be wrong)
According to the OSG the maximum fault current likely to be found in domestic properties in the UK (unless in heavily built up areas) is 16kA.

However this is probably stated because annex Za of BS60439 provides an additional test, for domestic consumer units that are protected by a BS1361 fuse at the supply, to ensure that a BS60439 consumer unit can take a 16kA fault current without danger.
This permits the use of protective devices in the consumer unit that may not have the short circuit rating to cope with the prospective fault current since the assembly as a whole will cope.
This is part of why the manufactures do not permit different makes of breaker in their consumer units, they say they are not tested for those units.
 
Here's our overhead supply for comparison and comment. Our transformer is served by two high voltage conductors, which in turn come from a string of poles carrying three conductors - ie two of the three branch off to our property. I assumed these were two phases from three phase, but comments here now make me unsure.

IMG_1402-CROP-1280_zps997c4e1c.jpg


One green/yellow sheathed cable comes from the case of the transformer into the ground on the N side of the pole.

IMG_1399-1280_zps7adfd9cd.jpg


On the other side of the pole the two cables out of the transformer join the underground service cable which goes to our meter cabinet. One connects via the isolator or fuse or whatever it is (the grey item), the other is clamped directly. After the join to the service cable, there's another earth that goes underground at the foot of the pole on the S side. The DNO guy who traced and marked the cable routes for us said that this would run some distance horizontally underground while still insulated, then further distance uninsulated.

IMG_1401-CROP-1280_zpsbbbeed37.jpg


Our earthing arrangement was described as "CEW" and also "TN-S" by the DNO engineer, after he opened part of the cut-out to check.

Tony S
 
Last edited:
Will do tomorrow, it's dark just now.
 
So does anyone have a picture of a PME system :joker: Seeing as freshman are bound to be seeing that old chestnut.
I know, I know, but the question will be asked, guaranteed.
 
This is another nice thread.
 
  • Funny
Reactions: DPG
This is another nice thread.
Sadly most of the contributors can no longer share their wit and wisdom with us, which is very sad.
 
  • Agree
  • Friendly
Reactions: pc1966 and UNG
Yeeeeah, some can though. ;)
 
If you have a neutral connected to an installations earth terminal (eg PME/TNC-S) then the incoming supply cables metallic sheath connection must be disconnected. Especially important where a supply cable is suppling both TN-S and TNC-S earthing arrangements!! eg, ....where the DNO cable is in the process of being PME'd....
Well Dan,on your recommendation ,I decided to read this thread (all 12 pages of it). Very interesting.Feels a lot older than 10 years.It also raised a question for me ,based on the comment above from "Engineer54". He suggests that the metallic sheath of a TNS cable must be electrically isolated as soon as the TNS supply is converted to TNCS.Why does this have to be done?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing Arrangements Explained + Photo's
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
177

Advert

Thread statistics

Created
Paul.M,
Last reply from
LastManOnline,
Replies
177
Views
152,842

Advert