Thanks for the reply - ‘NO’



How would you get around discrimination between a 30mA protecting buried tails & RCBO’s tripping?
I can’t see a workaround other than mechanical protection or a 16mm SWA with in-built mechanical protection

Thanks for the reply - ‘NO’




That's pretty much the size of it. 522.6.204 (i) to (iv) are your options, earthed SWA/conduit/trunking/MICC etc, or very strong mechanical protection.Thanks for the reply - ‘NO’
How would you get around discrimination between a 30mA protecting buried tails & RCBO’s tripping?
I can’t see a workaround other than mechanical protection or a 16mm SWA with in-built mechanical protection![]()
Yep….That's pretty much the size of it. 522.6.204 (i) to (iv) are your options, earthed SWA/conduit/trunking/MICC etc, or very strong mechanical protection.




BPG4 is giving this situation a C3, so wouldn't necessarily need remedying:Yep….
That’s where I am…
BUT
I’m going to fit a 100mA to buried meter tails as remedial EICR work.
OK, it’s not to regs …. Shoot me.
A 30mA may discriminate - rendering the fancy RCBO board useless.
If Joe bloggs were to ---- a meter tail I’m sure they’d welcome any form of RCD opposed to the 60A DNO fuse tingle?
Common sense to me - I’ll say that in court should the need arise
Explain to customer & admit to deviation on certificate.
Case for the defence rested m’Lord…![]()
Yep… understood!It will only discriminate if the earth leakage, including 'normal' leakage from all the circuits, is below the tripping threshold of the 100mA RCD, typically 60 - 70mA.
If the earth leakage is above this, then both the relevant 30mA RCBO and the 100mA supply RCD will trip.
….



Yeah…. I just don’t think it’s safe for meter tails at potentially 100ABPG4 is giving this situation a C3, so wouldn't necessarily need remedying:
C3 - Absence of additional protection by RCD for cables installed at a depth of less than 50 mm from a surface of a wall or
partition where the cables do not incorporate an earthed metallic covering, are not enclosed in earthed metalwork, or are not mechanically protected against penetration by nails and the like.