Hi All

I am having 24V Led lights installed in my garden. Its 12m in length drawing power at 16W per M.

The LED comes with 0.5mm of tails which i want to extend.

The distance from the strip to the LED driver is 25m in a single length.

Using online calculators to gauge which sized cable i need, its recommending 10mm or 16mm SWA cable to stay under 3% voltage drop but this seems excessive to me.

For info: My LED Driver is 230V Input, 24V output. Rated up to 350W Supply.

Can anyone advise?
 
Yes that is the kind of cable size you would expect for that.

You will also probably have issues with voltage drop along the length of a single atrip 12m long and fed from one end only,
 
its recommending 10mm or 16mm
There is a massive difference between the two sizes 'IT' (Online Calculator?) cant recommend both. Its got to be one or the other, given that the same installation criteria for the formulae.
I would suggest you get a local electrician to size the cable properly.
 
There is a massive difference between the two sizes 'IT' (Online Calculator?) cant recommend both. Its got to be one or the other, given that the same installation criteria for the formulae.
I would suggest you get a local electrician to size the cable properly.
Two sizes as there’s two install locations with varying cable runs. Shorter run has a 10mm recommendation. Longer run has 16mm
 
Can you not use a constant current led string and driver?
That would remove the volt drop calculation and just require the cable to be specified for the max current of the driver.
 
Can you not use a constant current led string and driver?
That would remove the volt drop calculation and just require the cable to be specified for the max current of the driver.

You would still need to ensure that the combined forward voltage of the LEDs plus the volt drop in the cable is less than the maximum voltage output of the driver.
 
You would still need to ensure that the combined forward voltage of the LEDs plus the volt drop in the cable is less than the maximum voltage output of the driver.
Agreed but, the calculator the op is using is trying to achieve less than 3% volt drop at 24v or about 0.75v
Even if the driver had a max of 32v that will give over 10 x the original volt drop allowance .

It would be worth speaking to the lighting supplier and specifying a system that works with sensible cable sizes.
It is somewhat ridiculous to be using a 16mm cable for a load less than 200w
 
Even if the driver had a max of 32v that will give over 10 x the original volt drop allowance .

We can't know that without knowing the forward voltage of the LEDs. We only know that they are configured to work on a 24V constant voltage supply at the moment.


To change to a constant current supply they would need to be re-configured into a series circuit which would drastically change the required input voltage.

It is somewhat ridiculous to be using a 16mm cable for a load less than 200w

Yes, it's completely daft, and with a little lateral thinking I'm sure it could be easily solved.
 
Well we know it's 24V at 192W = 8A

What's difficult about a CC 8A source capable of 33V using 1mm² cable?



Apart from the 70W loss.


Splitting the run in half and running it in series on 48V will bring it down to 4mm²
 
Last edited:
Well we know it's 24V at 192W = 8A

What's difficult about a CC 8A source capable of 33V using 1mm² cable?

24V 192W when configured for a constant voltage supply.
The load would need to be reconfigured in order to operate it on a constant current supply.
To operate reliably on a constant current supply all of the individual LEDs would need to be connected in series, The voltage required from the cc supply would be the sum total of the forward voltages of those LEDs.

If you connected an 8A cc supply to the load as it is then it would most likely destroy the LEDs sooner or later.
 
24V 192W when configured for a constant voltage supply.
The load would need to be reconfigured in order to operate it on a constant current supply.
To operate reliably on a constant current supply all of the individual LEDs would need to be connected in series, The voltage required from the cc supply would be the sum total of the forward voltages of those LEDs.

If you connected an 8A cc supply to the load as it is then it would most likely destroy the LEDs sooner or later.
Not until they start failing, then yes.
 