Not until they start failing, then yes.

They will fail fairly quickly as the cc supply is supplying too much current to the LEDs nearest to the supply. Once one has failed the current through the others will increase and the process of staging the LEDs will speed up.

Current from the cc supply will not divide equally between the parallel connected LEDs, the resistance of the conductors connecting them will affect the current distribution and lead to excess current flowing through the first set of LEDs, destroying them.
 
The most efficient way to run high power LEDs is using a series circuit with a constant current LED driver. Running a series circuit helps to provide the same amount of current to each LED. This means each LED in the circuit will be the same brightness and will not allow a single LED to hog more current than another.
 
Last edited:
I thought these were led strings so the leds are effectively in parallel?
Can you provide a link to the leds?
Are you sure it's 16W/metre that sounds very high?
Is your supply constant voltage or constant current?
You'll need to either split the length into 2 or power from both ends.
If you split into 2 you could use 2 lower rated supplies (I would, more availability and cheaper)
I don't understand why you would need SWA for 24v when much cheaper low voltage cable will suffice?
 
If it were me I'd get that driver moved closer to the strip, if running a 16mm swa is not an issue there must be a compelling reason why the driver can't be relocated
 
Unless I've misunderstood wouldn't it make more sense from a £ point of view to use muti stranded in a conduit and put the power supply indoors ? And I doubt the lighting strips would look any different at 4 or 5% less volts anyway (say up to 1 ohm for the cable).
 