Discuss Cable Size for 100m Shed Run in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
11
Can anyone recommend a good Cable Size calculator to use online?

The old man wants me to order some 6mm 3 SWA to feed his shed that will go on to supply some sockets, fairy lights around the garden and other stuff, no power tools or high load activities.

Cost is the mitigating factor here because the cable run is (his estimate) 100m (my estimate is 70 meters) from Consumer unit to shed running through the full length of his bungalow attic, down one side of the house and that ran along the kick board or bottom of his fence around the side of his garden.

Im thinking it might have to be 10mm which is going to put the job past his budget.
 
work out your load current. probably be no more than 20A if that. then calculate the VD for 6.0mm.
 
Also Doncaster have a similar one:
 
If looking at, say, 10A max load and a 16A B-curve MCB then Zs max is 2.2 ohm, assuming TN-S max of 0.8 ohm then 1.4 ohm for R1+R2 or 14mOhm/m for a 100m cable run.

Looking at the 2-core SWA for mucho cheapness, then
  • 6mm is 3.1+7 = 10.1 mOhm/m
  • 4mm is 4.6+7.9 = 12.4mOhm/m
So either those should be fine. Assuming 16A B-curve MCB/RCBO of course!
Also assuming the SWA is properly glanded to get a good and reliable connection to the armour!
 
If you work with 10A and 95m then the calculators come back with 4mm. Yes, below a 13A socket but for the expect use-case not a big deal. Seems also for 13A and 70m.

Of course you would use LED lights now so I don't think the 3% drop traditionally applied there is anything to worry about.
 
If looking at, say, 10A max load and a 16A B-curve MCB then Zs max is 2.2 ohm, assuming TN-S max of 0.8 ohm then 1.4 ohm for R1+R2 or 14mOhm/m for a 100m cable run.

Looking at the 2-core SWA for mucho cheapness, then
  • 6mm is 3.1+7 = 10.1 mOhm/m
  • 4mm is 4.6+7.9 = 12.4mOhm/m
So either those should be fine. Assuming 16A B-curve MCB/RCBO of course!
Also assuming the SWA is properly glanded to get a good and reliable connection to the armour!
please could you in light use how you got to this equation .
 
please could you in light use how you got to this equation .
Starting point was the light load, so assume enough for a 13A socket and not much more. So Table B6 of the OSG has Zs limit at 2.2 ohms for 16A B-curve MCB.

Usual assumption for supply Ze are 0.35 ohm max for TN-C-S and 0.8 ohm max for TN-S, from OSG page 63. So for a probably worst case (and ignoring the TT elephant for just now) we need Ze+R1+R2 to be less than Zs

R1+R2 = Zs - Ze = 2.2 - 0.8 = 1.4 ohm

The OP had the length as 70-100m so assuming 100m case then the max cable R1+R2 = 1.4 / 100 = 0.014 ohm/m or 14 mOhm/m (or ohm/km if you prefer).

Next went for the Prysmian SWA data sheet here:

Page 5 (last page) has a table of conductor and armour resistances. As the OP was worried about the cost, cheapest is going to be 2-core SWA assuming the armour as CPC is acceptable. So looking down the table we have:
  • 4mm conductor = R1 = 4.61, 2-core armour = R2 = 7.9
  • 6mm conductor = R1 = 3.08, 2-core armour = R2 = 7.0
Rounding to 1 digit we have the R1+R2 values as 4.6+7.9 = 12.4 and 3.1+7.0 = 10.1 ohm/km (or mOhm/m) for those cables types respectively.

Since both are less than the 14 mOhm/m from the first half, both are going to meet the Zs requirement for 100m or less length. Or you could work it around another way using length = (max R1+R2) / (cable R1+R2) so:

  • 1.4 / (12.4/1000) = 113m max for 4mm 2-core
  • 1.4 / (10.1/1000) = 138m max for 6mm 2-core

I would add a bit of margin though as those are DC resistance values, for 50Hz AC they would be slightly higher, but in both cases they look fine for 100m & 16A B-curve MCB.
 
Can anyone recommend a good Cable Size calculator to use online?

The old man wants me to order some 6mm 3 SWA to feed his shed that will go on to supply some sockets, fairy lights around the garden and other stuff, no power tools or high load activities.

Cost is the mitigating factor here because the cable run is (his estimate) 100m (my estimate is 70 meters) from Consumer unit to shed running through the full length of his bungalow attic, down one side of the house and that ran along the kick board or bottom of his fence around the side of his garden.

Im thinking it might have to be 10mm which is going to put the job past his budget.
 
@TimGemm
Most cable size calculators just do the current and volt-drop limits, for example:

Proper design is a lot more complicated (see above) as you also have to consider fault-clearing times and any minimum CPC size if you are bonding "extraneous conductive parts" when the supply is TN-C-S (most common for new homes in UK).

Generally if in doubt get a local spark in to sort it out. many of them will be happy for you to do the donkey work of trench digging and cable installation so long as they have oversight on the choice of cable and the installation at both ends.
 

Reply to Cable Size for 100m Shed Run in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
841
Getting desperate to clear my small garage, and I have a bit of old red/black T&E. I used a few bits to add a socket or two in my flat and a...
Replies
5
Views
1K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Morning, I was just looking for some advice on what other sparks would do for the following scenario:- A detached Garage is going to house a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock