BillyH

What options do i have for terminating a 16mm 3 core swa into a plastic consumer unit?
 
are you using the 3rd core as cpc? if so, then the armour only needs earthing at the supply end.
 
Hi,

You could terminate the swa into a seperate box that you would mount near the cu, then in the box, you would conect it to t&e via choc bloc, terminals etc. Then the t&e would go to the cu.

Cheers

Jay
 
just glandf the SWA into the CU, and then use a banjo, bent at 90deg to allow lug to be attched inside of the CU. This will reduce your Zs, and will take an extra few seconds. its not good practice to introduce joins in a cable, where there will be no need. As for not using a gland, this is also bad practice, unless the accessory is designed for the purpose, eg, some street lights.
 
agree^^^ best not to introduce joints if not necessary. but deffo use a gland. make sure SWA is well supported close to the CU so as not to put a strain on the box around the gland.
 
The cable will be installed in stud wall at 1st fix stage so would only be able to enter consumer unit through the back
 
Try and fit a conduit box to the consumer unit,it can be fixed securely reducing strain on the cons unit and allow the termination of the Swa to be done
 
Try and fit a conduit box to the consumer unit,it can be fixed securely reducing strain on the cons unit and allow the termination of the Swa to be done

that is a good idea by des, and you can still use a banjo if you wish on the bush on the inside of thje CU. If it was a smaller cable, you could use the 4mm lug hole in the back of the box
 
Personally i would never convert a SWA cable to T&E in an adaptable box in this circumstance. If you mount the metal adaptable box directly under the CU enclosure connected via plastic or metal coupling or other, you can then make your SWA termination off with a banjo or earthing nut to the box and take your conductors straight through to the CU, ....Sorted!!


As stated above, introducing unnecessary joints is never a good idea, especially when talking about the larger sized of domestic cables.

I've never seen street lighting with a means of earthing SWA cables without making use of a gland, and can't picture them either. you can't clamp them, without putting undue stress on the internal conductors. If anyone has a link to these accessories, i'd be interested to have a look at them.... Some of the worst corrosion i've seen on SWA cables have been at street lighting positions...
 