3 phase dis board for split phase

Discuss 3 phase dis board for split phase in the Electricians' Talk | All Countries area at ElectriciansForums.net

lewlec

-
Reaction score
8
hi all

just wondering, is there anything wrong with using a 3phase dis board for splitphase? i have seen a couple of installes about like this.

cheers.
 
What do you mean by split phase?

Using the board to power single phase circuits?

This is ok aslong as all phases remain balanced, by which I mean pulling the same amount oif current per phase
 
hi

460volt beetween phases & 230 between L1 & N & L2 & N.
Yes all single phase loads, just wondering what the best way is 2 x single phase boards or 1 x 3 phase board and double up on the main incomer.what are your thoughts?
 
I ve seen a three phase board used, you can just blank off all the spare ways , with some boards you can get a doubble pole MCB if you wanted to run any single phase 400v loads at a later dae, another reason for usingone board in sterad of two
hope this helps
AJ
 
Hager do a single phase link kit for their 3 phase DB's.

All you need do is cut one tab off the link and install across two phases in the DB.
 
Hager do a single phase link kit for their 3 phase DB's.

All you need do is cut one tab off the link and install across two phases in the DB.



I feel that would not be good practice as you would have an un ballanced board also the manufactuer didn't design it to be used like that
 
I feel that would not be good practice as you would have an un ballanced board also the manufactuer didn't design it to be used like that

Really cant see a problem.

One phase would carry for eg 100A and the remainder spread across the other 2 board phases.

As long as its properly labeled, it should be fine..
 

Reply to 3 phase dis board for split phase in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock