oldtimer
Got a call this morning the lady said I have been told to contact an electrician as I have no earth How do you know that i said well she said just had my suppler in who has put a new head end in and he has told me I will have to get a 16mm cable put in ok I will be down in 5 i said.
Got to the house and sure enough there was the new head end with a new MET as well there was a 4mm earth going from the DB to the old earth strap that was wrapped around the incoming supply cable. So I tested the Zs of the nearest socket and got 10 ohms the Ze was 0.09 ohms now the 4mm cable was 150mm from the new MET and there was enough on it for it to be temporary connected to the MET now yes it is not big enough but surely it would have been a lot safer rather than leave it as is.
Also yes they made a nice job but they did not fit a main switch no wonder or trade is a mess she even had an old meter so yep in about a years time they will change it and again will not fit a main switch. I thought it would have and should have to fit a main switch if the meter or the head end was being upgraded.
Put the 16mm in and the Zs was 0.30 ohms
Got to the house and sure enough there was the new head end with a new MET as well there was a 4mm earth going from the DB to the old earth strap that was wrapped around the incoming supply cable. So I tested the Zs of the nearest socket and got 10 ohms the Ze was 0.09 ohms now the 4mm cable was 150mm from the new MET and there was enough on it for it to be temporary connected to the MET now yes it is not big enough but surely it would have been a lot safer rather than leave it as is.
Also yes they made a nice job but they did not fit a main switch no wonder or trade is a mess she even had an old meter so yep in about a years time they will change it and again will not fit a main switch. I thought it would have and should have to fit a main switch if the meter or the head end was being upgraded.
Put the 16mm in and the Zs was 0.30 ohms