oldtimer

Got a call this morning the lady said I have been told to contact an electrician as I have no earth How do you know that i said well she said just had my suppler in who has put a new head end in and he has told me I will have to get a 16mm cable put in ok I will be down in 5 i said.

Got to the house and sure enough there was the new head end with a new MET as well there was a 4mm earth going from the DB to the old earth strap that was wrapped around the incoming supply cable. So I tested the Zs of the nearest socket and got 10 ohms the Ze was 0.09 ohms now the 4mm cable was 150mm from the new MET and there was enough on it for it to be temporary connected to the MET now yes it is not big enough but surely it would have been a lot safer rather than leave it as is.

Also yes they made a nice job but they did not fit a main switch no wonder or trade is a mess she even had an old meter so yep in about a years time they will change it and again will not fit a main switch. I thought it would have and should have to fit a main switch if the meter or the head end was being upgraded.

Put the 16mm in and the Zs was 0.30 ohms
 
I was doing aquote for a rewire and I took a look at there service head. Well it was old, with a porcelain fuse with 30a written on it. I didnt pull it to check if it was 30a or had been replaced by a bigger one,(well im not allowed to pull the fuse, ill get my pandys smacked), any way the main earth was a bit of 2.5mm stripped from from a bit of twin. I told the customer to get in touch with DNO and tell them it needs upgrading. A few weeks later I got a call from the customer saying an engineer had been out and moved the service head to down in the cellar fitted an isolater and even put a sticker on it with the Ze reading, earthing arrangement etc and did the main bonding to gas & water. When the customer asked how much it cost, the engineer replied, "because the main earth needed upgrading, it wont cost you a penny because its up to us to maintane it but if you would have rang and asked us to move its position to your cellar, then it would of been around £2000." Well the customer was well happy that I brought it to there attention and I got the job. Some DNOs are ok, or I must of got luky with this one.


Jay
 
Last edited:
So how does your DNO say its up to them to maintain a good earth yet the opinion from DNO's are we are not responsable to supply you an earth and if you want one it will cost.

My post above was meant to convey a rant at these clowns because as i said it is perfect timing to fit a main switch whether you are fitting a new head end or a new meter. Mind the only bonus was that I got the job to put a 16mm earth in and I am not complaining these guys are under pressure I get that so they are told dont get involved with the consumer side but the least they could have done was to put the 4mm to the new MET and said get an electrician
 
Last edited by a moderator:
Scottish Power are very fly regarding earthing

I have had several conversations when upon asking about earths they say it will cost- even if you call regarding an existing one

Only when you specifically point out that the earth was existing and as such it's part of their newtork and their responsability do they actually offer to come out
 
I am planning a CU change in my own house and rather than pull the fuse I thought I would contact EON regarding a DP isolator. They are coming out on Thursday to fit one free-of-charge. I'm assuming they will upgrade my earthing to 16mm to the MET as it is currently 6mm on a PME system.
 
EDF don't fit isolators (oh and they didn't turn up when I booked them to come in so I could fit an isolator)

Well, I spoke to UKPN about it and they said "No, EON will do that for you". Whoever they sub to, it was EON who I dealt with.
 