Wow! I was going to reply to original post but i don't think i will now after all the arguments!
Thanks for providing this info and for clarification.
Although classing each flat as a seperate installation when there is only 1 DNO supply , only 1 gas main and only 1 water main is open to debate in my mind.
At the moment we do not know the earthing arrangement of the premises.
If its PME then table 54.8 comes into play re the bonding and if TNS or TT the csa should be not less than half the csa of the required earthing conductor with a min of 6mm!
NO, ... There is nothing to debate at all!!
Agreed , but table 54.8 applies to the main protective bonding ,which is in the basement , where the gas and water services enter the building.
Not relevent to where the services enter each flat.
Unless your suggesting that there needs to be 2 sets of main protective bonding conductors , basement and flat ?
I do like a healthy technical debate lol.
A very narrow minded view you've got there.
To Add,
If each flat is PME, the earthing conductor to each flat has to be a minimum of 35mm, (again sized to the DNO's incoming Neutral), as it has to satisfy as a combined CPC and main bonding conductor (Pg 52 GN8).
Really, perhaps you can tell us what's narrow minded about following requirements??
And if you think about it, why it's a requirement!!!