Wow! I was going to reply to original post but i don't think i will now after all the arguments!
 
So , taking onboard recent comments....
What size should this protective bonding conductor in the flat be ?
Just out of interest ...
 
At the moment we do not know the earthing arrangement of the premises.

If its PME then table 54.8 comes into play re the bonding and if TNS or TT the csa should be not less than half the csa of the required earthing conductor with a min of 6mm!
 
According to GN8, the main bonding is sized to the DNO's incoming Neutral supply cable, not the downstream local neutral supply cable to the individual flat, it should not be less than 35mm in the case of PME supplies.
It is a little odd in the the main bonding conductors can have a greater csa than the local Live supply (to each flat CU) conductors.

In all other cases (TT, TNS) the main bonding is sized to be not less than half of the Earthing conductor.

At least that is how I read it (GN8).
 
Last edited by a moderator:
Thanks for providing this info and for clarification.
Although classing each flat as a seperate installation when there is only 1 DNO supply , only 1 gas main and only 1 water main is open to debate in my mind.

NO, ... There is nothing to debate at all!!
 
At the moment we do not know the earthing arrangement of the premises.

If its PME then table 54.8 comes into play re the bonding and if TNS or TT the csa should be not less than half the csa of the required earthing conductor with a min of 6mm!

Agreed , but table 54.8 applies to the main protective bonding ,which is in the basement , where the gas and water services enter the building.
Not relevent to where the services enter each flat.
Unless your suggesting that there needs to be 2 sets of main protective bonding conductors , basement and flat ?


I do like a healthy technical debate lol.
 
But each flat has it's own main bonding requirement.

I will be glad when the new GN8 comes out, as it is a nightmare trying to marry up the 16th ed reg no's with the current regs.
 
To Add,

If each flat is PME, the earthing conductor to each flat has to be a minimum of 35mm, (again sized to the DNO's incoming Neutral), as it has to satisfy as a combined CPC and main bonding conductor (Pg 52 GN8).
 
This is getting to be like pulling teeth...lol!!

Every flat, (be there 2 or 20 flats) will each require a main protective bonding installation, REGARDLESS of the main protective bonding arrangements made at the buildings service head and main distribution centre and where the main services enter the building (eg, gas & water).
 
Last edited by a moderator:
Agreed , but table 54.8 applies to the main protective bonding ,which is in the basement , where the gas and water services enter the building.
Not relevent to where the services enter each flat.
Unless your suggesting that there needs to be 2 sets of main protective bonding conductors , basement and flat ?


I do like a healthy technical debate lol.

Main protective bonding conductors are required in every flat in Multi Occupancy Premises regardless to what is connected outside that premises!
 
To Add,

If each flat is PME, the earthing conductor to each flat has to be a minimum of 35mm, (again sized to the DNO's incoming Neutral), as it has to satisfy as a combined CPC and main bonding conductor (Pg 52 GN8).

But the flats aren't pme , tt , tns or anything else , they're supplied via a privately
owned sub-mains ? so not entirely relevent.
 
Really, perhaps you can tell us what's narrow minded about following requirements??

And if you think about it, why it's a requirement!!!

I didnt say the requirements were narrow minded , just your view that an wider issue cant be discussed openly.
 