devonsparky
I always get different views on this one.
I'm wiring a shop (commercial premises) and have done the install in conduit and through p-clips above the ceiling tiles.
My understanding of the regs is that all TN systems must meet 0.4s disconnection times. (Table 41.1)
Any of you guys got any input on this one?
Or 5s disconnection time for circuits above 32A.
Which circuits (if any) require RCD protection? If any do, assuming it's a three phase system then use RCBO's on those circuits and MCB's on the rest if cost is a factor. If not, RCBO the lot.
I'm not entirely sure I fully understand the question but I hope that helps in some way.
Cost is a factor but as it's going to be a spar shop, I don't want nuisance tripping and constant call outs.
I was thinking of putting an rcbo on the cleaners sockets but was going to mcb the rest (lights, cooker, fly killers etc)
Didn't want to rcbo the till sockets or computer sockets because of the same reason.
I just want to be sure that I'm not going against the 'bible' on this one as I have to certify it.
I have been mainly a domestic installer so am still interpreting the commercial side.
Thanks for any feedback
Sockets must have rcd protection. If the others are in conduit and are not on special locations that need rcd protection then mcbs will be ok
if the staff of the shop are considered to be "skilled or instructed persons" then no need for RCD if the disconnection times are met by the MCBs. i do work in a few spar shops and none of them have RCDs.
All socket outlets require RCD protection unless fed individually and labelled for a specific purpose.
I would probably not consider any staff at a Spar skilled or instructed persons so I personally would avoid using that one.
IMHO, RCBO any socket circuit. If the installation is done well, there shouldn't be any nuisance tripping.
You say that you work primarily within the domestic sector, just a pointer mate, the regs are the same no matter what sector you work in.
Out of interest, is it a single or three phase installation?
I'd say there skilled at stacking shelves!
'Skilled person' basically means qualified supervisor, like in a factory who would have a permanently employed electrician, no spar would have one!
It is a three phase installation.
I'm going to rcbo all socket circuits but mcb all the others.
I do understand that the regs apply to all sectors but also know that for domestic installs, you adhere to the building regs etc
On TN systems, your Zs values should be such, to allow a MCB to disconnect that circuit within the permissible times. That is the rule whether there is an RCD in circuit or not. It should never be solely down to the RCD device to protect a circuit against earth faults. They are classed as Additional protection, whether they operate before an MCB or not!!
Far too many out there, are now relying on RCD's where the maximum Zs for a circuit(s) hasn't been met to meet ADS times. In fact they are relying on RCD devices for all manner of things these days, where they shouldn't be!!
Yeah, you're right Engineer54, RCD's seem to have clouded everyones thoughts and took their eyes off of the fact that it's the MCB that has to meet the disconnection times.
So, as long as my MCB's meet the disconnection times they are ok ....................... RCD protection is additional protection (as per regs)
Agreed!
However our ECA assessor says we can have loop impedances up to 1667 ohms as long as the circuit is 30mA protected.
But what happens when the RCD fails?
Just a couple of things devonsparky, you mention you're a DI, are you insured to work on three phase, check your policy documents if not sure as it's important that you are. Also, are you confident you know what you're doing? I'm not having a go as I don't know you but the suggestion that you want to omit RCD protection from socket outlets seems to me like you need to read through the regs book a few more times.
Like I said, I don't know you so have no idea of your level of knowledge, I just wanted to check that you're confident to do what you're planning to do :)
ha ha ............... yeah fair point 'D Skelton'.
I'm just a sparky who gets twisted and tied in knots sometimes and I guess I interpret the regs my way but listen to others who feed me different ideas/advice etc
I'm actually an approved electrician (C&G 2360/NVQ 3/C&G 2391) and an Approved Contractor with the NIC EIC so yes, can legally work on any installation.
But I respect your point as some questions do come across as 'green' from time to time but I like to hear different thoughts from people ......................... and if you read the posts that come back on any given question, there are some very different levels of advice !!
How do I know you have the background/qualifications etc to take your 'advice' ???? lol
devonsparky,
bartkusal,