I like the sound of that C&G 2360... lol!!!
(C&G 2360/NVQ 3/C&G 2391)
ha ha ............... yeah fair point 'D Skelton'. I'm just a sparky who gets twisted and tied in knots sometimes and I guess I interpret the regs my way but listen to others who feed me different ideas/advice etc
But I respect your point as some questions do come across as 'green' from time to time but I like to hear different thoughts from people

How do I know you have the background/qualifications etc to take your 'advice' ???? lol

Very worrying.Agreed!
However our ECA assessor says we can have loop impedances up to 1667 ohms as long as the circuit is 30mA protected.
However our ECA assessor says we can have loop impedances up to 1667 ohms as long as the circuit is 30mA protected.
if the staff of the shop are considered to be "skilled or instructed persons" then no need for RCD if the disconnection times are met by the MCBs. i do work in a few spar shops and none of them have RCDs.
you do not need rcd protection on these sockets. you only need to provide an rcd socket for use by cleaner/workmen etc. the shop workers are skilled or supervised persons. and the fabric of the building will be worked on by skilled builders. this is stated in 7671
you do not need rcd protection on these sockets. you only need to provide an rcd socket for use by cleaner/workmen etc. the shop workers are skilled or supervised persons. and the fabric of the building will be worked on by skilled builders. this is stated in 7671 and the on site guide. disconnection will be achived by mcb,s
you do not need rcd protection on these sockets. you only need to provide an rcd socket for use by cleaner/workmen etc. the shop workers are skilled or supervised persons. and the fabric of the building will be worked on by skilled builders. this is stated in 7671 and the on site guide. disconnection will be achieved by mcb,s
Disagree on this. you cant class a shop worker as skilled or supervised person. Skilled is electrician, supervised is supervised by skilled person, that is electrician. And then comes the resident engineer,if there is one you dont need rcd anywhere, but that has to be agreed on design stage of installation and well documented...
The
You can disagree all you like and try to interpret who is and who isn't skilled or supervised or instructed....but your wasting your time.:banghead:
It is a Statutory LAW (EAWR and H&S Legislation) that Employers have a duty of care to provide training and supervision/instruction to their Employees along with risk assessments which may include prohibiting the use of personal equipment in socket outlets etc etc......therefore the Spar employees must be Instructed Persons By Law and as such RCD protection is not required as stated in BS7671 which by the way is non-statutory. Any sockets used by ordinary persons will be a different matter.....:wink_smile:
Then by your argument, every employee in every shop, office, school, library, police station etc..... every employee in every business or establishment where there are sockets that exist without RCD protection is an instructed person. IMHO, that is not the case. No matter how much training is given to a shelf stacker on how to use a non RCD protected socket outlet, it still doesn't make them an instructed person.