M
mljc71
Hi All- New to this - loving the challenges!
EICR'd my house and found one of my ring finals had an IR problem- just getting to grips with testing and trying to gain experience- college was good, however, felt like it was more of learning to pass exams!
My ring final has an issue- if i test with breaker open-(off) L(load side of breaker) to E (earth bar) = good reading, N(neutral bar) to E= good reading- but L to N a bad reading. so if a possible dead short between L-N why doesn't breaker trip?
However, if i do a IR L and N to E i get a good result!
Sorry for my inexperience but can anyone help me?
What is the result between L/N? You say a dead short, so is the reading 0.00Mohms? Sounds like you may have something still connected like a spur that you may have missed.
Jay
Make sure you have disconnected all appliances, especially freezers and fridges. A low Ir reading doesn't mean you have a short.because you are dealing in Mega ohms.
nope checked that- has spots in bedroom connected somewhere, but left that part of circuit open,
why a good IR reading with the L-N to E:?
thanks for the reply
lol lots of diy bodges (not mine)! even got an off peak socket! spur'ed off eco10 lol
Sounds like a load still connected, neon in a spur or something, could you have a spur in the loft for something if you've got some DIY stuff there.
definitely sounds like something still plugged in, did you do end to ends on ring final as had similar when i moved in - one side of ring and immersion heater feed transposed so low ir reading ( imm and ring on 32a mcb and 16a mcb nearly got zapped changing imm stat so did pir and found lots of horrors - funny had just been passed by council contractor)
Also the reason you'll have a good reading between both live conductors to earth is because there's obviously no fault to earth hence why it seems like an appliance plugged in because otherwise your ring would trip.
ty for replys only 2nd post i think!- will investigate further in loft- also for experience going to take all sockets off and connector block them- do a bell test to check continuity then do IR test- end to end- then cutting circuit into 2 and so on.
caus your not testing through a load....
check for TV aerial amplifier or shower pump when your in the loft have come across this several times recently
Because if there was a fault to earth you would have a reading between l+E and or N+E but because there isn't a fault present you will get a good reading, because you're getting a reading between N+L this either means there is a fault but more likely you're getting the reading from a load and the connection between L+N is across the load
If your getting a good reading when connecting L&N and testing to Earth then i wouldn't be losing any sleep over it, However as mentioned above the readings defiantly insinuate that something is still plugged in to warrant poor readings. If your L&N to earth is over 1.0 meg then as long as your record how its been tested on the test sheet then that's sufficient.
With an IR that low the only conclusion is something is still connected. You have to be very observant doing this job properly or you'll be going round in circles....
mljc71,
GLENNSPARK,