I have just tested an existing ringmain starting with the line conductor reading 0.32 and the neutral reading 0.87, these are both in 2.5 twin and earth, can someone explain why there is a big difference in the 2 readings when the conductors are the same size?
 
R2 or r2? and it's not a ring main. it's a ring final.
 
its a ringmain as i did end to end continuity, with the conductor been the same size surely the readings would be the same more or less
 
go round the ring....get them joints checked ....also check the test instruments leads and batterys.....dont forget to null em out properly (not through hinges).....
 
so the high reading on the neutral will be down to loose connections?

the reading is higher as theres more resistance on the nuetral, if it's old install is there loads of round, brown junctions under boards with loose connections??
 
None of the result sound correct, i'd re-test and see what you come up with. Make sure you have your test leads connected properly and nulled as suggested earlier
 
Looks like r1 is a little high too if your r2 is 0.28, its got loose connection written all over it or dodgy test leads mine gave me some funny readings the other day so I changed them now there perfect
 
i would say about 18yrs old, there is only odd JB, there is approx 14 sockets on the circuit
 