Paul_K

Hi guys, I'm new here so go easy! :-/

Need some advice on a shower that keeps tripping the breaker!

I have a 9.5kw shower running on 230v supply with a type B 32amp breaker. I've taken a measurement using a clamp (Fluke i410) from the wire at the consumer unit and it's measuring about 36amps and not the 41.3 as the calculation would expect. This problem appears to be too much current?

My question is this:
Can I safely put a higher rated breaker in, say 40amp, using the existing wire? I think it may be 6mm, but not entirely sure.

Much appreciated,

Paul.
 
Depends on what size cable is supplying the shower, what the derating factors are etc! Distance of the run!
 
if the cable is 6mm and clipped direct, then a 40A MCB would be suitable. this assumes that no part of the cable is covered by insulation.
 
I'd hazard a guess and say between 10-15 meters, as the consumer unit is downstairs, and the shower upstairs! :-/
 
Use the advanced editor or link the URL to photobucket or something. What is the cable size?
 
my guess is this is a shower upgrade done on the cheap and on 6mm cable protected by 32A breaker and i would hazard a guess you need to upgrade cable to 10mm and breaker to 40A no way would i ever run a 40A on 6mm but that's me.
 
i would hazard a guess you need to upgrade cable to 10mm and breaker to 40A no way would i ever run a 40A on 6mm but that's me.
Why would you hazard a guess?

6mm² clipped direct is rated at 47A and nearly five times the csa of 45A fuse wire.
 
Hi all,

To be honest I don't know if it's 'clipped direct' or not, or what the installation method used is!! We've only been in the house just over a year and this has been a recurring issue since moving in with this shower. It normally only trips if you're in it longer than say 10 mins... :-/

Steve, I can't attach links yet as I'm just newly registered on the forum. Apparently I need to post 6 comments first!
 
Where about are you? Someone one here may be able to drop in and offer specific advice, and if appropriate change the breaker. Is the breaker covered by an RCD?

Regards.
 
Everyone who comments on this thread is hazarding a guess as the OP has not give the full info needed
That may be true.

However, the quote also contained "no way would i ever run a 40A on 6mm but that's me".

There seem to have been several posts lately where 'electricians' do not trust the regulations and install cables which are larger than necessary 'just in case'.

If it complies, it complies.




 
perhaps 25mm tails just to be on the safe side:presents1:
did you get a cert when the shower was installed?
 