S
Sparkattack
Recently looked at a job to relocate a pump due to the poor location it was in for maintenance purposes. The current set up is a 230Va.c centrifugal pump rated 0.77KW 3.4A FLC fed from c type 6amp MCB to 16amp switched socket.
Am I right in saying that this needs to be changed to incorperate a DOL starter with overload protection as the motor is greater than 0.37KW? Or is the current set up ok?(reg 552.1.2) The motor will be constantly running as it feeds water to monitoring equipment and will have infrequent stop/starting.
Let me put it another way.
What does a DOL starter do, how does it operate?
Direct starting through a contactor/overload. DOL-Starter.gifWas thinking 230v version sized to suit
Most DOL starters are 3 phase.
They basically switch 3 phases at once allowing full current to the motor when switched.
Some are often used to allow remote starting, perhaps the motor is somewhere in a high ceiling or on a roof, and you need to be able to switch the motor on from down on the floor.
Some are used to reverse direction.
If a motor has too high an FLC, a DOL starter will not be suitable, and a soft starter, changeover starter, star delta starter whatever you want to call them will be required.
Just trying to interpret reg 552.1.2 as it mentions electric motors exceeding 0.37KW shall be provided with control equipment incorporating means of protection against overload of the motor.
The MCB will provide overload protection but its not classed as control equipment?
read the second sentence of that reg. the motor is incorporated in the pump, which as a whole complies with BS.
I see as the motor and pump are one unit which as a whole comply with a BS Standard the first part of the reg is not required. Got it!!
Thanks for your help
Hi the way I see it the motor will still need overload protection, what happens when something fouls the pump or motor bearings start to seize up motor could burnout before mcb trips
Unless the pump motor has integral or incorporated thermal protection/cut out, a starter with thermal protection, should in my opinion always be provided. Relying on an MCB will never give you the close thermal protection required by the majority of motors...
It was originally a breakdown i was asked to look at as the water sample had stopped. The motor on the pump was red hot! This is what what brought to my attention there being no thermal protection.
I will be fitting a DOL unit with overload.
Sparkattack,
Brightspark2,