It will trip on continuity of N+E

Say you turned the mcb off and cut the cable the rcd would trip.

Sounds like it was most likely something plugged in.
 
It seems the House Holder has removed a faulty bit of equipment like an Iron, or something, or you have corrected the fault when putting the Neutrals back in the correct RCD places maybe, or did i miss the point LMAO its l8 for my old eyes.
No and no! I removed all loads prior to testing and tried every appliance or portable equipment available in the house when finished. All circuits were removed one at a time and replace as found. The installation was fine up to the point the rcd tripped and would not reset even with all line conductors removed, and it is fine again now.
 
Wet joint box somewhere?
8 megs aint good, especially if it is only l-e and not on n-e.
In an occupied and dry house IR should be better.
Have you tested end to end yet?

Boydy
 
No and no! I removed all loads prior to testing and tried every appliance or portable equipment available in the house when finished. All circuits were removed one at a time and replace as found. The installation was fine up to the point the rcd tripped and would not reset even with all line conductors removed, and it is fine again now.

The neutral and earths are still connected though arent they....it stops tripping when you turn off the main switch because you are then isolating the neutral.
 