Thanks chaps! Now have the major headache of trying to sort some bonding!!! May have to make do with a connection back to the DB earth (25/4 SWA) instead as the METs about 100m of serious building work away.
If the supply at source is PME, the 25mm 4 core SWA installation is will not be sufficient as a bonding conductor!! You have a choice, run a separate bonding conductor back to the MET or install a TT system for the whole swimming pool installation. If TN-S your in luck, depending on the Zs values on a 100m of feeder/supply cable!! lol!!
What's the betting no-one provided a connection to the pools re-bar, or to link out from the re-bar to any metallic steps supports, or d/board supports?? lol!! That in it's own, would have given you more than a half decent Ra!!
You may not be out of the woods yet!! lol!! Has the floor slab reinforcement been earthed/bonded, only ask because as the back of my mind somethings telling me that on PME supplied areas, where bare feet are going to be the norm (swimming pools/saunas/spar's etc) such buildings need a bonded floor grid!! I may be wrong Rockingit, so give it a quick check in the books ... lol!!