6mm clipped direct just on the limit, but you'd need a OCPD of 50A, so 6mm is out of the equation. 10mm on a 50AMCB is your only choice.
11kW @ 230V = 47.8A
11kW @ 240V = 45.8A
Whichever way you look at it 6mm² will not be sufficient because the CPD will need to be a 50A MCB as Tel has already stated.
You need to state how the cable is run however, because the environment the cable is installed in dictates how much it is de-rated by, and you could end up with 16mm² if your running it in fully insulated spaces or in an environment subjected to external heating.
Guys, what about this kiddy...
Redwing 12kW Shower
Personally I say 16mm² will be sufficient on a 286m run, but the Regs work it out to be a 120mm²...anyone any thoughts...Muhahahahahaha :D
I got asked to install one of those once and his "mate" who was an electrician but out of the country at the time said it could be spurred off the ring :D i couldn't see a problem and i only had 1.5 with me at the time so i used that, do you think it'll be ok? I did change the mcb to a 50A too cos it kept tripping that poxy 32A :D
Some of these showers are turning mental, it's got to get to a point when you can't really heat the water much quicker under standard water pressure?
anyone living next door to the jones's who have a 10kW shower. just plain snobbery.
Christmas day mum has the cooker going full pelt and dad decides to make her a cup of tea and a slice of toast and at the same time daughter steps into the 11kw shower thats when you find out if your 60A DNO fuse will be ok lol
The OP occupation is stated as Gas so at a guess he's either got bad wind or he's a plumber and with all due respect to the kind nature of this forum he really needs to get a competent electrician on site as oppose to taking a few tips off here and doing it himself, any missed info could be vital to the safety of this install and he clearly hasn't any electrical experience with the basic form of his question...... do the OP a favour boys and recommend a sparkie to weigh it up you haven't spent years training and learning all this to do all the calcs for a DIYer /plumber working outside his trade.
Dare I venture to suggest getting a sparky in?
Or has the OP gone away?????????
I think I found him..
I have a 43.9kW shower...well actually it's a 150,000 BTU Potterton Boiler...That is only wired on a 1.5mm² flex from a 13A spur, works fine!! (I think the gas connection helps though!)
It will do more than work fine ... It'll knock the spots off any domestic electric shower any day of the week, any time of the year.
The same loony who surprises you with an 11 kw range oven with induction hob, warming draw twin oven and grill after saying its a double oven and gas hob......
Bit of 6mm and a 32 it is, then. ;)
11kw shower cable size?
Chris14,
DPG,