6mm clipped direct just on the limit, but you'd need a OCPD of 50A, so 6mm is out of the equation. 10mm on a 50AMCB is your only choice.
 
11kW @ 230V = 47.8A
11kW @ 240V = 45.8A

Whichever way you look at it 6mm² will not be sufficient because the CPD will need to be a 50A MCB as Tel has already stated.

You need to state how the cable is run however, because the environment the cable is installed in dictates how much it is de-rated by, and you could end up with 16mm² if your running it in fully insulated spaces or in an environment subjected to external heating.
 
more like apocolypse now. wait for the 10kW cooker cable questions.
 
Guys, what about this kiddy...

Redwing 12kW Shower

Personally I say 16mm² will be sufficient on a 286m run, but the Regs work it out to be a 120mm²...anyone any thoughts...Muhahahahahaha :D
I got asked to install one of those once and his "mate" who was an electrician but out of the country at the time said it could be spurred off the ring :D i couldn't see a problem and i only had 1.5 with me at the time so i used that, do you think it'll be ok? I did change the mcb to a 50A too cos it kept tripping that poxy 32A :D
 
Some of these showers are turning mental, it's got to get to a point when you can't really heat the water much quicker under standard water pressure?
 
anyone living next door to the jones's who have a 10kW shower. just plain snobbery.
 
Christmas day mum has the cooker going full pelt and dad decides to make her a cup of tea and a slice of toast and at the same time daughter steps into the 11kw shower thats when you find out if your 60A DNO fuse will be ok lol
 

Reply to 11kw shower cable size? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi , I’m going install a commercial 450mm extractor fan , what size and type of cable should i use ?
Replies
7
Views
376
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
664
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
862
Hi what cable make and size would be needed for hikvision cctv cameras 2.8mm model number DS2CE72KF3T-E picture provided
Replies
8
Views
404

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock