jwc

Second question of mine on here and it's one I've never got round to getting an answer for.


Mains comes into a building through a 60A main fuse for instance.
Why then are main switches rated at 100A or 80A?
Does this mean any load above 60A would blow the main fuse before it blew the main breaker?


Don't be harsh people. I'm fully aware the answer's probably an obvious one.
 
Last edited by a moderator:
you are confusing the main switch with a fuse. the rating of the switch is the max. load it will carry. it is not an overcurrent protective device
 
Hi. The answer is in the terminology. When you write "Why then are main fuses rated at 100A or 80A?" you probably mean "Why then are main switches/RCDs rated at 100A or 80A?"
The switch rating is not related to your supply rating (but needs to be same or more)
 
60A fuse will happily run @ 80A for about 1 hour. that's why you have a switch rated above the fuse rating.
 
Just received an inbox stating that the main switch doesn't trip on overload? :/
Really? Thought the main switch was essentially an MCB to carry the load of the other MCB's if that makes sense?
 
How? haha.
I just wanna know what's the point in having a main switch with a higher rating than the main fuse which supplies it?
Surely you want your main switch to disconnect before the main fuse blows?

If your main fuse is 60A, main switch is 100A, and your house is pulling 80A, what use is the main switch?
 
Just received an inbox stating that the main switch doesn't trip on overload? :/
Really? Thought the main switch was essentially an MCB to carry the load of the other MCB's if that makes sense?

totally wrong. the switch is a 2 pole switch, nothing more. each circuit is protected by it's own MCB. the installation as a whole is protected by the DNO fuse. think of the switch as your car. it will do 110 mph, but you run it at no more than 70mph.
 
JWC - Its hard to respond to a question sometimes without been harsh but im scared to the fact this question comes up numerous times from 'Qualified' Electricians now im starting to think you in yourself are not to blame here but either your tutor or the course itself .... may i ask what kind of course you have taken... now you realise that the main switch is just a mechanical switch and nothing more its brings to question are other areas of your learning lacking in basics ..... this could be dangerous in design in some situations if you thought the main switch on a standard dist-board afforded overload protection.

Hope you dont take as a dig at you...

To note hear you can get main switches although usually in larger commercial and industrial boards that do afford overload protection 'MCCB's and or a combination of earth leakage protection.... maybe this is where you may have confused yourself, but your bog standard 17th edition board DP switch is exactly that - a switch without the perks.
 
Thanks for the explanation, Darkwood. I've completed a full apprenticeship, AM2 and NVQ Level 3. Everything's much clearer now knowing that the main switch is exactly that... A switch.
 
On a similar vane I had an electrician with 2391 who carried out a PIR and recommended that a 40A 30mA RCD should be changed to a 32A one, asked him why he replied because the fuse protecting the circuit is only 32A thus it would go before the RCD if the was an earth fault and not the RCD as it was rate at 40A, shook my head and walked away in disbelieve
 
There is a simple reason for switches being 100A.... They can be used on a system with a 60A fuse, an 80A fuse, or a 100A fuse. In other words, one size fits all.
As already said, a switch is just that, the same way as an RCD is just that...they do not "trip" on overcurrent. While I agree that nobody knows everything, this is pretty basic stuff.
 
I was refraining from saying anything, but it seems like the rest of you haven't held back! I agree with jamesBoater. how can the OP not know this basic knowledge after having gained said quals?!
 
Thanks for the explanation, Darkwood. I've completed a full apprenticeship, AM2 and NVQ Level 3. Everything's much clearer now knowing that the main switch is exactly that... A switch.
FFS and people on this forum lambast Electrical Trainee!

Stick a 63A Main switch in and everyones happy?! ;)
 
trev your'e the last person I'd think of a racist. Tell em to **** in their hat and punch it! (not a very scottish term, but its what came to mind) :)
 
a lot of domestic propeties have a 100a main fuse so why do many domestic boards have 100a main switch then 80/63a rcds surely there is potential for overload under fault conditons or am I missing something silly?
 
ok good point but isnt that similar to say a 10 amp lighting circuit with 5amp switches in different rooms surely the light switch is underated and could be overloaded under fault conditions?
 
I understand what your saying but think of a ring it is wrong but you come across a 20 amp double pole switch which feeds a single socket for appliance the appliance is fused but you would have to change that double pole switch a its only rated to 20amp but under fault conditions could pull 32amp so if this is wrong whats the difference with a 100a fuse supplying downstream an 80 amp rcd with no downrating? I understand what your saying about balancing the load but why are they not 100a rcds inline with modern cut out fuses? also light switches do far more than 1 light in commercial and rooms with downlights etc a lot of old switches are five amp if your doing eicrs too
 
@Bigshow84
Explain your fault conditions you refer to.... a short will see a possible current over 1000amps this will operate the protective device in a time that damage isn't caused to the cables, accessories etc

You can spur a single socket direct off the ring you wouldn't fit a 20DP switch, the fuse within the plug top will limit current ... see appendix 15
You keep saying fault conditions but your are not specific by what you mean....

Following the regs you would not design a circuit capable of giving a small overload for a long duration, please explain this fault that is getting you confused.
 
Last edited by a moderator:
im scared to the fact this question comes up numerous times from 'Qualified' Electricians now im starting to think you in yourself are not to blame here but either your tutor or the course itself

Oit! remove those apostrophies from the word 'Qualified' :D



Not neccessarily mate


How could such knowledge be missed or not taught if you have completed all the above, and gained the qualifications!
I was refraining from saying anything, but it seems like the rest of you haven't held back! I agree with jamesBoater. how can the OP not know this basic knowledge after having gained said quals?!

With the standard of training available today, it isn't surprising that this simple bit of knowledge is often missed. Believe me, I know!
 
Not neccessarily mate

With the standard of training available today, it isn't surprising that this simple bit of knowledge is often missed. Believe me, I know!



i hope you're wrong D. if a time served spark is installing main switches based on their overload capabilities, then the trade's in a worse state than we all imagined.




EDIT: and to avoid confusion, by "overload capabilities", i mean ability to interrupt overloads.
 
Last edited by a moderator:
Whats even more worrying is the large schemes out there be it Nappit, Elecsa or Niceic etc all welcome them with a golden ticket and fuel this dumbing down of the industry ...its all ok expressing they have stringent strict guidelines to gain entry but means nothing when you ask the wrong questions and allow the member to pick and choose the jobs you can check..... if they ever were done by you in the first place.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Obvious question more than likely.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
76
Unsolved
--

Advert

Thread statistics

Created
jwc,
Last reply from
shagbite,
Replies
76
Views
5,851

Advert

Back
Top