Today I have come across a recently rewired house and I noticed that the installing sparky has indicated on the Install Certificate that the lighting circuit is T&E 2 core 1.5mm and CPC 1.5mm. However, I have noticed that in fact there appears to be several runs where T&E 2 core 1.5mm and CPC 1.0mm has been used instead.
From a testing point of view it is fine and Max Zs is well within the Regs guidelines. I am just wondering 2 things and despite checking my regs cant find any 100% answer.
1. For the certificate - should it actually have been issued stating the smaller T&E 2 core 1.5mm and CPC 1.0mm rather than as it is now T&E 2 core 1.5mm and CPC 1.5mm?
2a) Am I obliged to advise the client that the T&E 2 core 1.5mm and CPC 1.0mm should now be replaced with the same cable as used in the majority of the lighting circuit, that is T&E 2 core 1.5mm and CPC 1.5mm
OR
2b) Can I simply leave it as it is and just advise the client that there is a mix of CPC size on the lighting circuit. Afterall the safety disconnect of the circuit is fine anyway.
Thanks to all in advance for your views.
Hi All,
OR
I didn't know that you could get 1.5mm T&E with a 1.5mm cpc I thought all 1.5mm T&E had a 1mm cpc.
As pennywise said, record the smallest value. it's quite common to see mixed conductor sizes. One common practice was to wire the circuit in 1.5 and use 1.0 f or the switch drops.
Hi - I've got the same issue at the moment: I'm, doing a pvc conduit installation using 1.5mm single core cpc on the lighting circuits in conduit (no supplier could get me 1mm single core), however there are places where I am going over to 1.5mm/1mm twin & earth outside conduit, where it seems sensible to do so.:) Is this OK?
(First post! - whew)
It's fine! Just record the smallest CSA on the cert, and you could also note the differing sizes too. If Zs are OK then what's the issue?
Reply to Lighting Circuit - Mixed CPC Sizes! in the Australia area at ElectriciansForums.net
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Hi, So I've just started to install some spotlights in a room in my house, and I always thought to use 1.5mm T&E so I've wired them all up and...