G
Gavsparky
Hi all, I need I little guidance on this particular system I have which is. I have a combi boiler with a L/N/E/SL I also have a programmer, 2 zone valves each operating upstairs and downstairs central heating which are on 2 separate room stats. Now say if I'm wrong but I can't see past the room stats if one was to call for heat then the other zone valve operating also as there is only 1 SL terminal at the combi. Sorry if this is hard to understand but this picture might help but like I say there will be 2 x room stats to operate independently. Cheers in advance.
Scrap that diagram it's no use to you.
Programmer enables the stats.
Each stat opens it's respective zone valve.
The open zone valve/s calls for the boiler.
Cheers for the quick reply. I realise that the room stats can operate each zone valve independently but as it is supposed to also operate the SL of the combi I can only see both zone valves opening together as they will both be connected to the SL?
Standard 's' plan set up with two heating instead of heating and hot water. Both oranges connected together as switched live to boiler enables either zone to fire the boiler when it's respective room stat calls for heat. The second zone valve will not operate due to having a 'backfeed' up the orange. Hope that makes sense.
Thanks for the help mate. My thinking was that if both oranges were connected to the SL to boiler to fire it up, then both zone valves would operate. Forgive me if I'm being dense!
You need the outputs from the controller going to the stats and when the stats call to open the respective valves.
Then using the internal relay on the valves (grey and orange), connect both greys to the unswitched supply and both oranges to the boiler call.
So if one stat is calling for heat it will open the respective valve, once that it open it will call the boiler and won't back feed the other circuit.
You probably need a wiring centre to house all the interconnects.
Brilliant I think I'm nearly there with that, the only question I have is where does the unswitched supply come from (grey) thanks mate
So to sum it up, we have a core from the controller supplying both stats then in turn, each switch wire from the stats will be connected to the grey of the zone valves respectively, then both oranges connected together will return to the SL of the boiler? Am I right in thinking
No.
Assuming both zones are controlled by one timer, call from the programmer goes to the stats.
Stat call goes to the respective valve (brown) to open the valve.
valve greys are connected to the supply for the heating (programmer supply - unswitched)
valve oranges are connected to the SL of the boiler.
I suppose the grey and brown of each valve could be connected together if you can't connect the greys to the heating unswitched supply.
Nope, that would tie the two stats together when both valves are open, backfeeding via the boiler SL and preventing one valve closing while the other stat is still calling for heat. Greys must be fed with permanent live.
My thinking was connect the brown of zone 1 (say) heating valve to the grey of zone 1 heating valve and the brown of zone 2 heating valve to the grey of zone 2 heating valve. Can't see how this would backfeed. In this case the greys are only live when the stats are calling as opposed to being permanently live.
Why not just wire it properly in the first place? Bring all the wiring together into a wiring centre, you need a permanent live for the boiler anyway so just as easy to do it right!
Not true, greys can be made live from SL backwards through valve microswitch. See pic, shown with both valves open. When stat 2 or its programmer contact removes the supply from valve 2's motor, the motor would remain energised via the path shown dotted until stat 1 is also satisfied. Then both valves would close at once. And vice versa of course.
Combi boiler wiring advice please
Central Heating Systems
Gavsparky,
Lucien Nunes,