lockhes

evening all

i fitted 2 lights with a pir sensor controlling each light both working fine when i left and for about a week, until 1 became faulty it comes on around just getting dark all fine but soon as it gets dark completley it wont pick anybody up.

so i replaced sensor last week customer rang up today saying same things happening again but other lights been fine all along seems odd having 2 faulty sensors bought few weeks apart

lights are a 2d fitting

any sugestions
 
Was the light fitting and sensor made as one unit or were they separate items that you've wired together?
 
seperate units i have wired together

there was an old light there which was switched so i blanked off switch and linked perm and switch together then to the PIR then to the light
 
sounds like you got a light source nearby working off a photocell, making your new sensor light think its daylight

ifnthis was the problem i would of thought the other 1 would have this problem as theres more surounding light in that area
 
I have no trust in those room occupancy PIR's, never found one that's been reliable enough to fit and forget yet....
Most last longer than a week or so though!! lol!! They are at their worst when switching CFL lamps, they just don't like em!!
 
GLD had this market sown up years ago with good quality external pirs and equipment. But now there seems to be real bad quality gear out there sold buy the local wholesallers.
 
Switching CFL lamps with a PIR is poor design option IMO if you sort your issue out youll be back in a few months time replacing the burnt out lamps.....

Ill agree with above your PIR may be saturated by another heat source and can't then see the passing source or its been set up incorrectly so you are not crossing the PIR but actually walking into it which can blind it to a persons presence... Id be fitting relay triggered PIRs with Led floods ... done loads of these and never been back to one.

I refused to fit PIR's in the past just to their reliability been poor.
 
Switching CFL lamps with a PIR is poor design option IMO if you sort your issue out youll be back in a few months time replacing the burnt out lamps.....
Quite Right, you will find the manufacturers recommend the lights are run for long periods with a sensor, short bursts just ruin lamp life and infact the control gear as well.
 
Quite Right, you will find the manufacturers recommend the lights are run for long periods with a sensor, short bursts just ruin lamp life and infact the control gear as well.

Just looking at a Hager PIR sensor (EE804/EE805) information /data sheet now, (the next manufacturers unit we are going to try) ....Nothing about recommending long on periods and short bursts ruining lamp life (but that would go without saying for any lamp type!!) etc just the sensors max Wattage for given types of lamps!!
 
Switching CFL lamps with a PIR is poor design option IMO if you sort your issue out youll be back in a few months time replacing the burnt out lamps.....

Ill agree with above your PIR may be saturated by another heat source and can't then see the passing source or its been set up incorrectly so you are not crossing the PIR but actually walking into it which can blind it to a persons presence... Id be fitting relay triggered PIRs with Led floods ... done loads of these and never been back to one.

I refused to fit PIR's in the past just to their reliability been poor.

These PIR sensors are for internal areas not exterior, normally in toilets and other infrequently used areas such as large/small storage rooms etc. Most internal type fittings, either being surface or recessed, are still generally based around fluorescent and CFL lamps of one description or another, unless were talking about small LED downlights, so it's hardly bad design, no-one is going to fit incandescent lamps these days are they... lol!!
 
well i went tonight to look at them and worked fine

i advised her on timers or photcell instead of PIRs as there always causing problems

cheers for help
 