Hi again,

a kitchen has been ripped out, the main water stop was in there. it was all lead and copper water pipes and a main bond was to be run. However matey has lopped these pipes off and left about 4 inches of lead pipe coming in and then gone and replaced with plastic pipes. so would the small length of remaing lead pipe need bonding?
 
Hi again,

a kitchen has been ripped out, the main water stop was in there. it was all lead and copper water pipes and a main bond was to be run. However matey has lopped these pipes off and left about 4 inches of lead pipe coming in and then gone and replaced with plastic pipes. so would the small length of remaing lead pipe need bonding?


It will indeed need bonding to the MET i'm afraid, as it's still introducing an extraneous earth into the property!!
 
Without seeing the area and taking into account other factors that may have a bearing on my decision I have to go with whats in the BGB and GN 8:
411.3.1.1 & .2 ..... SHALL connect to the M.E.T extraneous-conductive-parts including...(i) water installation pipes.
GN8 ...... ALL e-c-p to be bonded to the MET.
 
That just down the road, worked there before .

I was asked to work in Belfast and Cork a few times in the late '70's & '80's and always refused, but looking back I wish I had done Cork.

I was tarring Cork with the same brush as Belfast and I was wrong.
 
this is a picture, i know theres a clamp on there, but its cream crackered and fairly seized up... and does it matter if the bond is before or after the stop cock, i know the continuity is there between the cock, but normally?.....i dont like typing cock so much either
 

Attachments

  • IMG_2059.jpg
    IMG_2059.jpg
    291.7 KB · Views: 135
especially since i=p/u has moved to scotland. LOL. :waving:
 
What's so bad about Belfast then?

Well they seemed to be having a bit of bother with lunatics running around with guns and shooting people through the knee caps at the time and I'm rather fond of mine.
 
this is a picture, i know theres a clamp on there, but its cream crackered and fairly seized up... and does it matter if the bond is before or after the stop cock, i know the continuity is there between the cock, but normally?.....i dont like typing cock so much either

Plumber dropped one there.

That short bit of copper after the old siezed-up stop cock is the ideal place to fit a new one and then continue in plastic.

Must have been done by a spark who "knows a bit" about plumbing !!
 