The three wire is an old way of N→E connection. It moves the LV earth rod away from the MV earth rod.

Come on Tony, please explain what CEW is in simple terms, maybe with one of your infamous drawings! (If you're feeling in a generous mood! :-) )
I just can't visualise it.
 
Just because you asked Archy

How it was explained to me at the EMEB collage.

Around each of the earth rods there will under earth fault conditions be a voltage gradient in the ground. In order for the MV and LV to be interconnected the LV earth electrode must be <2Ώ. Higher and the site is referred to by the DNO as hot and no direct MV→LV earth connection is allowed.
Therefore the LV earth has to be moved away from the MV equipment earth. This is to prevent a MV earth fault migrating to the LV system.

My drawing for OH supply
OHearthingzones_zps22959b1b.jpg



DNO drawing for ground mounted
Substation_zpscacb0f7a.jpg
 
Just because you asked Archy

How it was explained to me at the EMEB collage.

Around each of the earth rods there will under earth fault conditions be a voltage gradient in the ground. In order for the MV and LV to be interconnected the LV earth electrode must be <2Ώ. Higher and the site is referred to by the DNO as hot and no direct MV→LV earth connection is allowed.
Therefore the LV earth has to be moved away from the MV equipment earth. This is to prevent a MV earth fault migrating to the LV system.

My drawing for OH supply
OHearthingzones_zps22959b1b.jpg



DNO drawing for ground mounted
Substation_zpscacb0f7a.jpg
and when you think about it Tony...its just common sense isn`t it...

differing potentials n all that lot...
 
and i`ll say this as well Tony..

one of the neighbours up until recently had issues with extranious in his house with voltage sitting on it..

then he said one day the DNO came out and were doing something...
ever since then the extranious in his house has been clear....

hmm.....
 
The DNO’s also have another crafty trick with MV OH earthing. You may have seen section switches on OH lines. If you look there will be an earth running from the switch metalwork to the ground. It isn’t a rod, there will be a mat.
The idea is that the ground the operator is standing on is at the same potential as the switch metalwork. Where it gets tricky is approaching the switch, I was taught “the shuffle”. You don’t go striding up to the switch as there could be a ground voltage gradient, you shuffle towards it not putting one foot fully in front of the other.

PS I don’t like MV OH lines.
 
Cows are more sensitive to the gradient effect because of the distance between their legs (this applies to some TV 'celebrities' as well). Luckily most cows don't need to operate MV switchgear - they normally stick the the LV stuff. Daz
 
PS I don’t like MV OH lines.[/QUOTE]

Oh boy, this is all filling me with confidence, not! So, as a poor soul who has to live with an overhead supply, is there anything I can do/have done to make it safer? Apart from avoid crawling about on all fours! The DNO is clearly not concerned until some poor sod discovers a fault!
 
The advantage of having sheep and cattle in the field is you know there’s a ground voltage gradient around the switch. Dead sheep and cows tend to give it away.
 
Oh boy, this is all filling me with confidence, not! So, as a poor soul who has to live with an overhead supply, is there anything I can do/have done to make it safer? Apart from avoid crawling about on all fours! The DNO is clearly not concerned until some poor sod discovers a fault!

If you know there's a fault, supplies gone off etc. Don't go nosing around the MV gear, simple as. If you're that woried, talk to the DNO. If you're on a farm then it's worth a phone call.

Remember I’m talking of fault conditions, not the everyday life of country folk.
 