nandrews87

Having a quick discussion in work with regards to sizing the main incomer of a three phase dis board. Can someone please tell me how the correct way to size the main incomer of a three phase board or single phase for that matter

Cheers

Folks
 
More details please! You have given us no info to the set-up and whether its domestic, commercial or industrial and what is the nature of the systems it supplies.
 
if you know the current requirements of the equipment it will be supplying its simple math and use of ampacity tables.
and its a matter of getting the proper hardware too
you should already be able to figure this out.
 
Its a three phase board so clearly commercial/industrial. Board would supply 8kw heater, 15kw cooker, 2 x 32amp socket circuits, 4 x lighting circuits and 3 x 32 amp commando sockets. its my opinion that a 125amp breaker would be enough based on previous experience but what I want is the theory/calculations to making such decisions.
 
This is the rule of thumb I normally use but giving this info is not available I presume there must be a method to work it out based on the load on the board
 
No but the loading of the new DB is.

besides, what was there answer to the said question?

There answer was to tally up total current from other loads and size main breaker on that number, I dont believe this to be right as it doesnt allow for things such as diversity factor. My approach is to size it based on device that provides protection upstream of the dis board in question but in this instance that info is not available.
 
edit ...deleted my page was stuck in the past so missed several post which answered what i was asking.
 
Last edited by a moderator:
Having a quick discussion in work with regards to sizing the main incomer of a three phase dis board. Can someone please tell me how the correct way to size the main incomer of a three phase board or single phase for that matter

Cheers

Folks

Don,t exceed the rating of the actual distribution board, in other words if the db is 100 amp rated then that's the maximum switch rating, if you have more load than that then you allow for a larger rated db yes?
 
3ph is no different from 1ph (you weigh up the loading on each phase)- your front end device should be rated for the load of the DB and Protected against overload of the supply cable, sorry but Im not really following what your asking exactly.

Are you asking how to determine loading of 3ph equipment like motors etc or how to balance loads .... hence more info i requested. Your question is too wide field to answer.

I am aware its not giving alot of info, Basically question is from an assignment giving to a lad I work with. Info giving is KW rating of 3 circuits, then asked to size sub circuit protection which is not an issue, also asked to size main incoming device and explain reasons why, thats where I feel more info is required.
 
Well you know the size of loads being connected to the DB, so your OCPD has to exceed them after diversity has been applied. Use the guides in the OSG for more info. Then simply use the equivalent or next size up main switch for the DB, not that difficult is it?
 
Thanks for educating me - 'Clearly, this is commercial or Industrial as its a 3ph board' .... don't get me wrong here we are the experienced educated members here.

Three phase boards thus supplies are found in domestic too ive done several over the years, we are trying to help you here so try not be so quick to denounce a question you are asked it was relevant to your query... on that note im out of here! Happy Learning.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 Phase Dis Board Incomer
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
nandrews87,
Last reply from
Darkwood,
Replies
26
Views
2,483

Advert

Back
Top