I live and work in France. In my humble opinion, the current regs here are in many (not all) respects better than the UK.
What I’m saying is don’t generalise
I got bored with all the cat fighting and haven't read the entire thread, so forgive me if I've said something that has already been said.
If you decide RCD is the way to go, Hager do a range of three-phase RCD's. They are not cheap, but you can often find them on ebay.fr second hand. There is...
Apart from the cost, which is small in relation to the rest of the install, why wouldn't you install an RCD if there is any doubt about the need, even if the regs do not require it?
Thanks for all the replies. I'll try and deal with them all one by one.
First, IR testing has not been done. My Megger is away at Fluke for recalibration and this being France, I don't expect it back for at least another 10 days. I can perhaps borrow one. Thanks for the thought, but if it is an...
Maybe I didn't make this clear. The earth (remember this is a TT system), is at the DP and was linked on to the pool area.
Rather than use this, a new earth was installed at the pool area.
I'm in France and this is my first post, so apologies if this is in the wrong section. Here is the problem.
I have a client, with a swimming pool and heat pump for the pool, but their main supply keeps tripping. The connection is:
* Supply companies incoming feed, three-phase, limited to 30A...