Hi guys I’ve got a motor starter I’ve come across and looking at the electrical drawings it’s originally had 35mm tails from a 100amp fused isolator switch. This has been replaced with 25mm tri rated cable. Looking at the specs for BS 6231 I can see the conductor can take 136 amps. Motors are 37kw. Is there anything I’m missing. How do you apply grouping factors for a panel running a single motor or is grouping factors not applied?

Thanks guys
 
Treat it as any other trunking for grouping factor. Consider ambient temp on panel and how often the load will be starting and stopping
If it’s 3 phase 3xsingle core and control circuits within the trunking how does this related to how many loaded circuits? Found this in bsen 60204-1
 

Attachments

  • image.jpg
    image.jpg
    413.1 KB · Views: 2

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Maintenance Electrician

Thread Information

Title
Tri rated cable and grouping factor
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
Jako13!,
Last reply from
Jako13!,
Replies
4
Views
3,244

Advert

Back
Top