Hello guys looking in,
Just want to make sure i'm doing this right as i'm still a bit fresh,
This is the senerio as follows,
Single lighting circuit from a 230v supply on a 10 Amp MCB.
1.5mm PVC Singles total length from board to furthest point 40 metres.
1500 total watts of various...
kathleenbilly
Thread
cable
calculation
looking
question
right
voltage
volts
Hi,
I was looking through old exam papers and came across the following question;
A 2-core distributor cable of uniform csa is loaded as follows:
Point B = 30A
Point C = 90A
Point D = 62A
The cable is supplied at End A at 229V and at End E at 231V. The resistance of the cable is 0.01...
if you were to work out the value of the prospective earth fault by calculation at point of the supply, what values would you need to do this calculation :confused:
Can anyone tell me how to calculate the zs in a 3ph+E installation as my tester will not give me a reading. I've looked into it and a special loop tester is needed, if this is right?
Thanks Paul
Appendix 4 in the regs has tables for Current-Carrying Capacity and Voltage drop.
I've used these many times with no problems, but i've never had to calculate a cable higher than 25mm.
when you look at cables 25mm and higher you see three values for mV/A/m (r, x, & z).
Using the calulation...
easymart
Thread
cable
calculation
current
factor
using
volt
volt drop
volts
Wondered if it would be of use to have a formula and calculation aid section, ie fill in the blanks and get the answeer type thing. :) Dont know how difficult it would be to do :o
Any opinions?
Hi all,
How do I work out the length of a circuit?
I have these figures
R1+R2 = 0.40
The circuit is wired in 2.5mm/1.5mm T&E
I take it I need to know the resistance of the T&E (where do I find this?)
Could someone give me the formula or point me in the right direction
Thank you.
Could anyone just confirm my results for adiquate earthing size and calculation using the adiabatic equation...
My test was on a ring main circuit wired in 2.5/1.5 pvc..
My supply voltage is 247v
My Impedance is 0.38 ohms.
The circuit is supplied via a RCBO 32a C type
My results suggest that...
Evening guys
When calculting ZS u us the formula ze + r1 + r2
So i have 0.18+0.60+1.00 = 1.78
But i also have my r1+r2 result which is 0.40
0.18+0.40 = 0.58
so which 1 do i use then?
Cheers guys. :)