Hi, as I've said many times on this forum, I'm not an electrician and now retired. I'm still keen to learn and spend a lot of time studying all things electrical (especially during this lock down madness - it keeps my brain active!!).

Anyway - I understand what Ib and In are and how they relate to each other when calculating cable size but I'm confused whether there is a difference between It and Iz?

Following on from that can you help explain why "the protective device operating current (I2) cannot be bigger than 1.45 times the current carrying capacity of the cable (Iz)."

Any help would be appreciated.
 
Coordination goes Ib (Design Current) must be less than or equal to In (Protective device) must be less than or equal to Iz (Current Carrying Capacity of conductor or It (Tabulated/Corrected Current carrying Capacity) (Electricians drive their Mercedes BeNZ uphill to Town (B N Z T, uphill = getting bigger)

You're wanting to ensure that your protective device and cable can handle the design current, and in the case of I2T not exceeding 1.45x Iz it's relating to the energy that the device lets though and, unlike It/Iz doesn't take into account resistance (hence the 1.45 factor to them take account of this resistance).
 
Thank you for taking the time to reply.

You say in your reply "be less than or equal to Iz (Current Carrying Capacity of conductor or It (Tabulated/Corrected Current carrying Capacity"). Am I correct in assuming that after correcting "Ib" to account for environmental and installation methods you arrive at "It". Then using "It" you look up the tables to get" Iz"? In other words "It" and "Iz" have different values - "Iz" equal to or greater than "It"

Still not sure about the 1.45 theory, You've given me something to work on though.

Thanks again for your help
 
Hi - here’s an article that might help :) .
 
Hi - here’s an article that might help :) .
Thank you for pointing me to this article but I've already read that. I fully understand conditions (1 and 2) but I'm struggling with condition (3) - I2 ≤ 1.45 Iz. I've followed several worked examples elsewhere (Chris Kitcher, SparkNinja) and they refer to It being derived from Ib and In making allowances for environmental and installation methods to determine cable size and I understand that as well, My question - is there a difference between It and Iz and can you explain what I2 is. This is purely a learning exercise for me but I'd appreciate any help you can give.
 

Reply to Cable calculation parameters in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
Replies
4
Views
4K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock