meter tails

  1. C

    UK New meter tails going under toilet cistern?!

    Hello, I am a customer, not a trained electrician! My adult son is overseeing some electrical work on the house. He got an electrician out who suggested upgrading the board (which was decades old) and doing an EICR. During initial discovery, the electrician found the meter's "tails" are too...
  2. J

    10+ meter tails

    Hi guys. I’ve just done an eicr on a flat and they need a fuse board upgrade. Now the tails are still 16mm and there protected by a 60a fuse. And the main cut out is 80a. Do I have to change the tails? The board is at least 10+ meters away, concrete ceilings, have to wire through boxing in, all...
  3. J

    UK Removing redundant meter tails yes or no

    I just bought myself a new house well old but new to me. Any way i have a nice old wylex rewireable DB to replace. Got permission off the distributor to pull the main fuse and go and collect tags once i am finished. Problem is it also has an old heating circuit on separate meter tails they are...
  4. M

    Can I use 16mm t+e Instead of meter tails as the board is miles away from the meter

    Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want it to have its own meter the meter was installed miles away from the consumer unit would I just use a Henley block or a main switch and use 16mm T&E...
  5. OnlQQker

    First I've Heard About These Screw In Meter Tail Connectors...

    Bit like those things you see clamped onto a water mains when people add an outside tap. Just a lot more dangerous by the looks of it on the electrical front...
  6. S

    Why do people get away with meter tails longer than 3 meters

    On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no other fused iso's/ or protection on the cables. Personally I use 25mm² swa and a fused isolator. Just want people thoughts??
  7. D

    Do these internally exposed meter tails require mechanical protection?

    Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another example online where this specific question that has been answered. What you can see in the attached photograph is meter tails (single insulated +...
  8. O

    UK Meter Tails : Do i have a potential issue?

    Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter, which was installed a couple of years ago (outbuildings on the second phase of a split phase supply) has been wired with 16mm tails but with a 100a...
  9. S

    Splitting meter tails at 3m

    I've haven't got a way back to the main supply and need to add a consumer unit for a garage conversion but the tails are on a double pole isolator switch so was going to split the tails at the 60a fused isolator about 2-3m from the main supply is there anything wrong with this or am I just over...
  10. I

    3 Types of Meter Tails

    Evening! Once upon a time I would use 25mm meter tails which comprised of 7 strands. I now use a 19 strand version. The other day, however, I'm sure I spotted a very fine stranded version on a page on YouTube or in a catalogue/magazine etc. Anyone know what this would have been and is it...
  11. N

    Meter tails no rcd in stud wall

    During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away. they do have an isolator but no rcd or other protection . as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally...
  12. M-B-Electrical-Services

    Correct process for meter tails upgrade and isolator install

    Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The consumer unit is an old MEM metalclad built in the 70's and requires replacement. The meter tails both on the supplier's side and consumer's side are...
  13. B

    Will a CT clamped on meter tails, energy monitor, get distorted by solar input.

    V.early days, just had installed solar. No battery, also supply of some parts difficult at the moment so no App or Online monitoring. I have a loop energy meter, clamped on the tail of the DNO electricity meter. Monitored use before solar & seemed pretty accurate. Looking at the inverter...
  14. C

    Can anyone identify these meter tails?

    Evening, Carried out EV charger installation survey today & found this meter. Is that a 16mm concentric type cable adapter between cutout & meter? This is a TT installation, tails unprotected. Not sure about installation method of DNO supply. I'd like to upgrade tails to 25mm between cutout &...
  15. T

    New meter tails running in 2 core 25mm swa and 16mm single earth

    Hi everyone, i might be having to run new meter tails from meter box to consumer unit which is just under 3m run, i have used 25mm 3 core before and its hard to work with especially through joists. I was thinking about 2 core 25mm swa and a seperate 16mm earth to make life easier but then came...
  16. K

    Mix of 16mm and 25mm Meter Tails

    Hi, Just had a new Smart Meter fitted yesterday along with isolator. The chaps installing the SMART meter used 16mm tails from the main DNO fuse cut out (containing 80 amp fuse) to the meter, but then used 25mm tails from the meter to the newly installed isolator (which they also installed). I...
  17. D

    Meter Tails Splice for EV Fitters

    What do we think..?
  18. C

    Best cable cutter for meter tails

    Which is the best affordable cable cutter for at least up to 25mm2 copper conductor?
  19. J

    Meter tails 10m long

    A customer has Rewired their house, and has run all the cables to a new a location they want the CU in, DNO has apparently told them, they can't move the incomers and meters without everything being tested and certified, creating the obvious issue that its not possible to test and certify...
  20. E

    UK Single meter suppplying 2 properties?

    New to the forum and first-time poster! Currently trying to confirm what the top meter (circled) in the photos supplies? To me, it seems the meter tails enter the connector block and then there are two outputs coming from the block - one to the top isolation switch and one to the lower...