i had a couple of sockets put in about 12 year a go and was thinking of adding another for tv on wall and was looking under floorboards and it looks like its done on a radial circuit as it come straight from the fuse box and ends at the 2nd socket ,it is also wired to the up stairs socket fuse...
I am a DIY and working on an extension on my home. I found out that one area of my house is on a 4mm radial for sockets on a 32amp mcb which I know is fine.
Now the question is
Can I safely continue wiring 4mm radial?
Total length from distribution to last socket will be around 60metres with 12...
Velascas
Thread
circuit
circuits
length
new
points
question
radial
ring
hi guys
Need some help in calculating voltage drop on a branched radial circuit. (13A design load 2.5mm cable)( cu to junction box 8m 2.5mm)
for a standard loop in loop out radial it would be IbxDxmV/m/1000
this circuit has 2 branches from the junction box
one/ 10m long ( 1 double...
Hi everyone looking to clarify something, had a tester onsite today testing circuits we've been installing the past few weeks, in his opinion he found fault with one circuit, we had wired a 30m radial circuit in 2.5mm 2core & earth fp200 on a c16 mcb. The cable was clipped direct throughout its...
Hi all,
I've tested several radial circuits and only getting 0.00 ohms on the r+r2 test (zero'd leads)
2 of the radials only supplies one socket each and are approx. 3 metres in total length. (zs 0.25 and 0.21)
Another radial only supplies one socket and is appox. 5m in length. (zs 0.35)
The...
I am currently renovating my kitchen and am considering swapping my standalone cooker for a hob/single oven combination.
Would it be possible to use a dual appliance output plate on a 32A ring?
The hob = 4.6Kw
The oven = 3.65Kw
or would they need to be on separate circuits?
Thanks
Hi all,
Today i found 2 radial circuits in a 32amp mcb breaker, would you give it a code c1 or c2 on a eic report?
Also what are the main dangers of having these together?
Cheers
Dem
Hi all,
I did some work on a house the other day that had a circuit for sockets which was cabled in 4mm to half way in the house the split of it to 2.5 up to the sockets. It had a 32a breaker. I'm aware that you can have a 32a 4mm radial but that the whole circuit must be in 4mm. Using 2.5 on...
2.5 mm radial t&e supplying 2 twin sockets on 32a Rcbo. Code2?
6mm radial to heater three phase nny-j cable, ccp of 42a on 50a mcb code 2?
2.5 mm radial t&e supplying one ac unit 32a mcb code2?
IN YTUBE
I NOT SHOWED ALL ASPECTS WHY !!!
MIDDLE POINTS DIFFERENT (picture below F2 and F1 radial frorces)
YouTube
>MAROSZ'S RADIAL TURBINE / TURBINA ROTACYJNA MAROSZA
Little scenario for you all.
I've been doing an eicr today and come across a double socket wired as a radial on a 2.5mm t-e, which is protected by a 32 amp rcbo.
Technically this cannot overload as the cable can withstand 27 amp ref method c. Unless mr DIY comes along and starts adding new...
hi i was on a fuse board change to day and the new fuse board was switch off and no buzz bar connected and no tails connected but 1 of the circuits which was a radial to the kitchen when you put the neutral in it tripped the rcd can any 1 tell me why :lightbulb:
Simple job to add an extra socket to top floor 'rfc'. Top floor was converted some 8-10 years ago but no certs available. Took Zs from socket I was going to spur from which was .6ish Ohm, turned off supply, proved dead then took end to end readings (at socket I intended to spur from) to prove...
Hi, I was going to post in the DIY forum but don't seem to have permission to at the moment. If i could ask a quick question - are you able to offer your opinion on my plan below:
I have a b16 circuit breaker in the CU for a radial circuit out to my garage. In the garage the cable feeds into a...
Hi
I have a Radial circuit wired with 2.5mm T&E , which is protected by a 3 amp MCB due to the fact that it is switched via a home automation relay rated at 5amp.
My question is this
Given the above scenario is it ok to install/wire a BS1363 socket if I know that the load that will be...
Evening Gents,
Im looking for some advice, I have to connect two convector heaters on a radial circuit - I will be connecting each outlet via fused spur flex outlet, I was going to use a 3x3 adaptable box to terminate the one armoured then connect in singles to fused spur...
Evening all
I've rad a few posts about running a radial off of a ring and there are loads of different options.
The problem I have is that we have no alternative as the customer already has a spur off the ring and wants a few more sockets but does not want us to start pulling about her kitchen...
Hi
I've just got to the end of a job in which I installed a 2way RCD protected CCU supplying 1x50a shower circuit and 1x16a radial circuit which consists of a 13a switched fused spur (outside bathroom) for a 2kw bathroom blow heater.
Typically now the job is finished the customer has decided...
I plan to install steel conduit (used as cpc) in a garage / workshop. I intend to run the conduit in a complete loop around the garage, i.e. starting at one point, going around all four walls and then back to the point at which I started. I want to do this because it makes wiring easier, i.e...