I seem to have located a radial circuit in the loft conversion. The Circuit is the Ring circuit from the Middle Floor which supplies only 4 single sockets on the Middle Floor, 2 single sockets in each room. In Each room there is a ring circuit and a spur.

My Problem is when i Removed 1 of the 3 double sockets in the loft and tried to do L/L, N/N and Cpc/Cpc, I got a reading on the cpc/cpc but no readings on the L/L or N/N. So I left the socket 1 disconnected and switch the power back on and tested the sockets. Sockets in room one - ring power ok, spur - no power, room 2 - power in both sockets, loft power only at the disconnected sockets on 1 wire only. When reconnected the socket wires I get power back in the spur in room 1 and the other sockets in the loft

The wire supplying the middle floor is the grey strand 2.5 mm and the one supplying the loft is white 2.5 mm T&E.

I have opened all the sockets in the middle floor and there is only two wires in one socket and 1 wire in the spur for both rooms - all in grey wires. There is no 3 wires in any sockets.

At consumer unit: Cpc to cpc - 0.41 ohm, L to L =0.34 ohm, N to N= 0.32 ohm. I also get a resistance of 0.56 ohm between the L and N ends.

With Figure of 8, R1+Rn in room one is 0.05 at socket wired as a ring and 0.66 ohm at the spur coming back from the loft, second room is 0.07 by socket wired as ring and 0.36 at spur socket and in the loft it is 0.47, 0.33 and 0.19 at the first socket.

R1+R2 is 0.12 at consumer unit then bedroom one 0.23 ohm at the ring, 0.86 at spur, Bedroom 2 - 0.47 at the ring socket and 0.19 at the spur socket and in the loft it is 0.63, 0.49 and 0.31 at the first socket.

IR - L to N - 0 (interconnection somewhere), L to CPC >299 and N to CPC >299 Mohms

I need to find out how to circuit is wired or where the loft connection comes from. My job was to add a couple of extra sockets as the loft conversion is being extended.

If not I might have to run a new circuit to the loft from the Consumer Unit. I have found a boiler in a cupboard in the loft at the end of the day as I was leaving, and a quick switching off the MCB for that circuit and the boiler was still powered.

Will appreciate any ideas or thoughts on this circuit.
 
I seem to have located a radial circuit in the loft conversion. The Circuit is the Ring circuit from the Middle Floor which supplies only 4 single sockets on the Middle Floor, 2 single sockets in each room. In Each room there is a ring circuit and a spur.

My Problem is when i Removed 1 of the 3 double sockets in the loft and tried to do L/L, N/N and Cpc/Cpc, I got a reading on the cpc/cpc but no readings on the L/L or N/N. So I left the socket 1 disconnected and switch the power back on and tested the sockets. Sockets in room one - ring power ok, spur - no power, room 2 - power in both sockets, loft power only at the disconnected sockets on 1 wire only. When reconnected the socket wires I get power back in the spur in room 1 and the other sockets in the loft

The wire supplying the middle floor is the grey strand 2.5 mm and the one supplying the loft is white 2.5 mm T&E.

I have opened all the sockets in the middle floor and there is only two wires in one socket and 1 wire in the spur for both rooms - all in grey wires. There is no 3 wires in any sockets.

At consumer unit: Cpc to cpc - 0.41 ohm, L to L =0.34 ohm, N to N= 0.32 ohm. I also get a resistance of 0.56 ohm between the L and N ends.

With Figure of 8, R1+Rn in room one is 0.05 at socket wired as a ring and 0.66 ohm at the spur coming back from the loft, second room is 0.07 by socket wired as ring and 0.36 at spur socket and in the loft it is 0.47, 0.33 and 0.19 at the first socket.

R1+R2 is 0.12 at consumer unit then bedroom one 0.23 ohm at the ring, 0.86 at spur, Bedroom 2 - 0.47 at the ring socket and 0.19 at the spur socket and in the loft it is 0.63, 0.49 and 0.31 at the first socket.

IR - L to N - 0 (interconnection somewhere), L to CPC >299 and N to CPC >299 Mohms

I need to find out how to circuit is wired or where the loft connection comes from. My job was to add a couple of extra sockets as the loft conversion is being extended.

If not I might have to run a new circuit to the loft from the Consumer Unit. I have found a boiler in a cupboard in the loft at the end of the day as I was leaving, and a quick switching off the MCB for that circuit and the boiler was still powered.

Will appreciate any ideas or thoughts on this circuit.

Boiler on its on dedicated radial? If it is could this be used for adding the two new socket outlets?
 
Last edited:
Will check exactly how boiler is connected when I go there next week. I might have switched off the wrong MCB or it could be wired into the light circuit. Did not see any new connections at consumer unit as all the wirings were original though consumer unit has been changed and some circuits RCD protected.

Also I would like to Know why I am getting different R1+Rn reading at each sockets when it should be r1 (0.34) plus rn (0.32)/4 should be about 0.16 ohms
 
Last edited by a moderator:
Not having a dig mate, but it probably would be better if the folks on here knew what they are dealing with, and tailor our answers accordingly, i,e, are you an Electrician, Trainee etc
 
The results do sound odd, though it is possible you had the ring interconnections for figure 8 the wrong way round.
However because the loft was a later addition and there are only two single sockets in each bedroom it is possible that it is an old spider ring that has been inappropriately modified to include the loft, perhaps by taking the feed from the spur in room one up to the loft and bringing it back round the loft and reconnecting back to the spur socket.
I have not thought it through in detail but the attached diagram is one possible way of getting results similar to yours, I have ignored the R1+R2 measurements as I do not know what you were testing there.
View attachment 29074
 
Hi Richard

Cannot open the attachment 29074 - not too sure why.

I had both wires completely seperate when doing the figure of 8 (there is not much wiring in the consumer unit) but will double check it. What is a spider ring as I cannot see the attachment?
Cheers.
 
Hmm do not know what happened there, the forum does seem to be messing up a bit at the moment.
I have reattached here.
I have also thought that your reading of 0.56Ω between line and neutral indicates that there is something electronic still connected to the circuit that is giving a false reading, if there were only 0.56Ω beween line and neutral then 400A of current would flow through the circuit when switched on and trip the breaker, so you may not have covered the whole circuit.
Ring plus spurs 50s possible.jpg
 
Hi Richard

Cannot open the attachment 29074 - not too sure why.

I had both wires completely seperate when doing the figure of 8 (there is not much wiring in the consumer unit) but will double check it. What is a spider ring as I cannot see the attachment?
Cheers.
a ring through jb's then a link from each jb to a socket
 
I have lifted some floorboards and looked at some on the wiring. I have found 2 juntion boxes in the corridor but there seems to be other spur wires going I do not really know where. The boiler was on that circuit as well. I have decided to run a new circuit for the loft sockets - instead to spending more time in sorting out this one and it will be quicker too as the staircases are being moved around on all 3 floors.

Thanks for you help
 

Reply to Radial Circuit off a Spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
621
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
613
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
259
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock