Nearly fifteen years ago I moved a bathroom in our house, and repurposed the 32A electrical shower circuit to power a pair of double sockets - which then had multiway adaptors powering all my office hardware (i.e. low overall power).
Not exactly complex or risky at the time, and the MCB has...
Doing an EICR today and customer has a tumble dryer in the shower room.
Room is an L shape with shower directly in front of door and around corner under stairs is a tumble dryer.
it is fed from a socket in the lounge next door, cable has plug on it in socket that goes along skirting through...
I have a pretty basic question on suitability of a shower digital mixer valve. Checked with the the manufacturer Mira, who insisted that it should only be used with their shower heads, etc. Asked why, looked around, etc but can't seem to find a clear answer why.
Basically I have read the manual...
My partner and I recently started renting a house.
The house comes with a Triton Enrich electric shower.
There's the usual pull cord connected to a box with a red light in the bathroom that turns power to the shower on or off.
However, does keeping it on 24/7 use much electricity?
My...
I have a solar pv system that has an Iboost fitted to send excess generation to my hot water tank. Combined with my solid fuel back boilers we almost always have hot water.
I also have a cold mains fed 11kW shower - not a power shower. I would like to feed the shower with luke warm water via a...
Morning all, I am working on a bathroom at the moment and the client has asked if the shower fan/light unit can be wired into a sensor instead of a pullcord switch (to activate fan when someone steps into the shower), I wondered if anyone has done any work like this before ?.
Apart from...
Hi all, I was with my senior yesterday doing a EICR for a domestic house. All of works are fine apart from this shower as shown below.
Shower is low and tiled around. I was suggesting to give it a C2 as water might get in contact for such low height. But my senior was saying it's just a C3...
Hi All
I have an issue with my shower and I suspect it's the solenoid.
The original fault is that the shower either wouldn't switch on at all, or it very briefly powers on, see video
I removed the front panel and as you can see below, manually pressing the plastic arm starts the water...
This may be one for the older members on here.
Got chatting with a mate about a general supplies to showers.
At the moment you just supply the correct size cable, (usually 10mm for a new circuit) to a shower.
Was there ever a requirement/regulation to add an additional earth cable along with the...
Hi guys
My tenant just had an electrician in to connect her cooker and has told her that the shower is dangerous and not to use it because it has a 40 mcb in the consumer unit and it should be a 32.
The cable is 6mm and the shower is 8.5kw.
Can you advise me please
Thank you in anticipation
hi all,
Thanks in advance for having a look at this problem.
Long story short, we have just moved into a new house. Unfortunately it’s transpired that the shower pump is also connected to the switch for the immersion heater.
I'm not a morning person at the best of times, but having to get up...
So I've been doing some work in a building and the fuseboard is located in a room which has been converted to a "multifaith room". It's basically a prayer room for Muslims as it's been kitted out with the facility to wash their feet and also a hand dryer mounted low level to then their dry feet...
I get regular work from a student landlord. In one of his properties the shower isolator switch has burnt out on the feed side several times. I've replaced the switch twice (last time with an MK) and the shower's also been replaced. Insulation resistance on the circuit is >500 and the MCB...
Hi. I fitted a new shower yesterday but it's not working. I don't know what's going on with it but it's strange. The old one is probably about 15 - 20 years old and before I fitted the new one I tested (with an electricians screwdriver) the black and red cables and they were both live. I...
Hi all, quick question, if I fit a new small consumer unit for a shower do I just test this board or do I need to test the existing house consumer unit as well ? Thanks Ian
Hey guys,
I'm currently doing my level 3 install qualification and I've been asked by someone to replace an electrical shower unit for them, now from my knowledge I am allowed to do said work as long as the power rating of the shower is the same as the old one and that it doesn't need a new rcd...
Hi,
Just want to get some clarification on something for my NVQ portfolio.
I have changed a shower & done the testing etc & have written this up for my portfolio.
In my write up, I said I safely isolated the shower supply via the shower isolator switch which was located in the bathroom next to...
Hello there! So we had a Triton Cara 9.5 Kw which was working OK for a couple of years and then the switch started burning a few times. Once we changed the solenoid coil and it was fine for a couple of months. But now the fuse tripped bc the switch burned and there is smoke after using the...
Hello. Can anybody please help. I've been in my house for 5 years and had no trouble with shower at all. A couple of weeks ago the wife says that shower wasn't working. I looked at circuit board and mcb had tripped. Flicked switch back on and everything was ok. Went for a shower later and its...