Hi guys

My tenant just had an electrician in to connect her cooker and has told her that the shower is dangerous and not to use it because it has a 40 mcb in the consumer unit and it should be a 32.
The cable is 6mm and the shower is 8.5kw.

Can you advise me please
Thank you in anticipation
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below
T

Toneyz

Is the shower protected by an RCD and is the cable under insulation would have a factor on the answer.
 

davesparks

-
Mentor
Arms
Esteemed
Ask for this to be put in writing by the electrician, explain that you need them to specify the exact regulation numbers which they are referring to and ask them to explain exactly how it is dangerous.

It 8s possible that the installation may not comply with the current regulations, but it may not necessarily be dangerous.
 

littlespark

-
Arms
Esteemed
Advent Win
The electrician was there to connect the cooker. He didn't have to mention anything about the shower circuit.
 
Sure that 6mm can only take more than 40A if clipped direct.
So a 32A would be a sensible option surely? 8.5kw is about 35/36 amps.
So smaller shower or bigger cable.
Or is my memory and maths failing me as much as my Fantasy football team?
 
  • Thread Starter Thread Starter
  • #9
Sure that 6mm can only take more than 40A if clipped direct.
So a 32A would be a sensible option surely? 8.5kw is about 35/36 amps.
So smaller shower or bigger cable.
Or is my memory and maths failing me as much as my Fantasy football team?
Hi Mike
I thought an 8.5 would draw a current of 35.5A so you would need an mcb higher than that and the next one up is 40.
Regards Chris
 

Dave OCD

-
Mentor
Arms
Esteemed
Chris, this is the correct sized MCB for a 8.5kW shower, a 32amp device would be running at a slight overcurrent and although it would take a long time to trip it's not permitted in the regulations. I can't stand people who find fault with work unrelated to what they're doing - especially when they're spouting BS. :)
 
  • Thread Starter Thread Starter
  • #11
Chris, this is the correct sized MCB for a 8.5kW shower, a 32amp device would be running at a slight overcurrent and although it would take a long time to trip it's not permitted in the regulations. I can't stand people who find fault with work unrelated to what they're doing - especially when they're spouting BS. :)
Thank you very much Dave for a very clear decision on this question.

Regards Chris
 

Paignton pete

-
Arms
Esteemed
The electrician was there to connect the cooker. He didn't have to mention anything about the shower circuit.
Dont think I agree there, if I saw a potentially dangerous situation I would point it out.

Saying that this is not a good example of that, as it's not a potentially dangerous situation.
 
  • Thread Starter Thread Starter
  • #13
Dont think I agree there, if I saw a potentially dangerous situation I would point it out.

Saying that this is not a good example of that, as it's not a potentially dangerous situation.
So you are sure it is not dangerous because I think my tenant will still want it changed to a 32 because an electrician has told it is dangerous and must not use the shower.

Regards Chris
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Shower 8.5 on a 40mcb is it dangerous in the Electrical Forum area at ElectriciansForums.net

SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom