Hello. How i should connect this 1 phase 2 pole 400v cooling pump? If i apply 1phase 230v and neutral it Will only growl and "spin" very very slowly.

Thank you for help.
 

Attachments

  • IMG_20231201_175321229~2.jpg
    222.4 KB · Views: 29
I know that, but typeplate says 1 phase thats whats confusing me. I measured My capasitor and its charging and decharging
single phase 400v is what the name plate is stating as the supply required.

this could be provided by a step up transformer if you only have 230v single phase available.
alternatively it is probably easier to get a 230v motor instead.
 
Typically 400V is obtained between two phases of a 3-phase supply (nominal 400V L-L /230V L-N) which is common thorough the UK & EU for larger installations.

What is the motor for, and why did you get a 400V one?
 
Typically 400V is obtained between two phases of a 3-phase supply (nominal 400V L-L /230V L-N) which is common thorough the UK & EU for larger installations.

What is the motor for, and why did you get a 400V one?
Its for pumping cooling liquid for bandsaw. It came with bandsaw but not working. It was installed ; L1 - L2. Now i rewired it L1 - L1 and now its working.
 
Its for pumping cooling liquid for bandsaw. It came with bandsaw but not working. It was installed ; L1 - L2. Now i rewired it L1 - L1 and now its working.
Have you verified that L1 - L2 - L3 are all OK and showing around 400V?

For it not to be working L1-L2 but now working on something else (I guess "L1 - L1" is a typo as that would be zero volts!) suggests L1-L2 was not 400V which on a 3P system is a fault.
 

Reply to 1 phase 2 pole 400v pump wiring in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock