just wondered if anyone can find this one as i couldn`t

A single phase ac installation from a lighting db contains a common conduit with 8 single core cables the grouping factor to be applied is

a 0.59

b 0.65

c 0.75

d 0.8

may be i was rushing but could not find one of these in grouping factors?

cheers

Tony
 
i'd go for 0.65. Table 4C1 "Note 3: factors apply to - groups of 2 or 3 single core cables"
8 singles....4 groups of 2...0.65 that's my reckoning anyway :)

could have 2 groups of 3 and a group of 2 which would give you 3 circuits and 0.70, but that's not one of the choices.
 
i'd go for 0.65. Table 4C1 "Note 3: factors apply to - groups of 2 or 3 single core cables"
8 singles....4 groups of 2...0.65 that's my reckoning anyway :)

could have 2 groups of 3 and a group of 2 which would give you 3 circuits and 0.70, but that's not one of the choices.


cheers pal think youve hit the nail of the head

cheers

tony
 