Discuss 2391-52 practical exam help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
hey everyone,
Wondering if anyone has done there 2391-52 practical exam lately i have mine this week just wondering a few things.
Rcd tests if i have a lighting circuit protected by a 61009 rcbo which point should the test be carried out at the distribution board or the accessory its self as i realise we are trying to reduce Live testing.
We have 2 lots of paperwork electrical installation cert & eicr we have been told that 2 circuits have been rewired which they will go on the eic but with regards to the eicr do we just leave the circuits black we here they have been removed to go onto the new eic cert? It’s a 3 phase Db which a circuit supplies the single phase Db?
Thanks for any help and if this is a stupid question again I apologise thanks
The two circuits for the EIC, will also be on the EICR.
You just copy the results on the EIC over to the EICR.
All dead tests will be conducted first.
Then they will energise the board for you to conduct the live tests, Ze PFC and RCD test.
I used the 3 pin plug lead to conduct the RCD test.
Remember to calculate Zs for all circuits after you have measured Ze.
Sorry, can’t recall whether the fault finding is before energisation, or after.
RCD test just at the end on one of the sockets with all the covers back in place. That is what I did.
For Zs I just calculated most circuits and I only measured on the circuits with sockets.
More of a safety aspect I guess instead of poking probes in ceiling roses live.
That’s it all complete PASSED.
Basically had 3 faults
my main bond was one of the faults giving a reading of 4.56 should be 0.05 or below
Next fault was the earthing conductor from the starter at the load side was broken basically you do a r1+r2 test to the top of the starter note it then at the bottom and add together for the total r1+r2 so from the load side it was broken so could not calculate zs as a result of this.
Last fault was on the ring circuit basically the conductors were all 2.5 L&N came back at 1.23 the cpc was 3.56 straight away this was noted meaning that our calculated zs would be to high so been recorded as a C2
Then paper work had to be perfect so happy it’s out the way and onto a new course thanks for the help appreciate it.
On the practical, we were told not to look for any visual faults as this was covered doing the photo exercise. My faults were high protective bond reading, open circuit on the lights and low IR.
Well done on passing but why should the R2 reading on the continuity of protective conductors be 0.05 ohms or below?
Guidance note 3 makes it clear that this reading is between 2 exposed conductive parts such as pipes and not from the MET to the bonding conductor.
It’s an urban myth badgered around the industry and taught incorrectly by the tutors
Reply to 2391-52 practical exam help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi Guys. Just wondering what people used to practice the written part of the 2391-52 exam? I have the iet exam prep book, which seems more geared...
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Hi - Just joined the forum as I'm making a career change and am training up. I've come across some mock papers online and am concerned that...