i need to wire in an induction hob which is 6.5kw and the cable already chased in is 4mm and would be a real pain to replace for a bigger. I just wanted to know if it would be alright or play it safe with a 6mm?
Well Ref B gives you 28A max on 4mm t&e and the appliance is unlikely to draw all its 6500W at the same time, so 4mm should be fine unless a more onerous installation method has been used.
Ok, clipped direct gives you even more headroom.
4mm clipped direct is 37 amps so depending on the installation method, 4mm is acceptable as I can't see zs being an issue if only 15 meters long.
Also diversity can be applied so the load is likely to be lower than 28 amps anyway.
The hob being 6.5kw - but what would it actually draw?
I've just been working on a kitchen where the customer sourced, induction hob, came fitted with a 13A plug!
Had one last month murdoch it was a siemens 4 zone and i was only armed with a cooker outlet plate :rage:
Change the out let plate for a socket. Simples
and i did after an unwanted trip to the wholesalers
Reply to 28A in 4mm cable 6.5kw hob in the UK Electrical Forum area at ElectriciansForums.net
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
A friend of mine wired a 10mm 3 core armoured cable to his shed before I got involved and wired it himself already. He wants make it an air bnb...
Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
4K
Hi all I'm in the process of swapping out my 4 zone CDA induction hob for a 5 zone Bosch. Currently the existing wire starts as a 5 core cable...