I'm thinking of quoting to :
1 - Install a MET (removing the crimp that was objected to).
This is probably worth doing just so it is there and a point for access/test. There is nothing in the regs saying bond cables have to be continuous, but it is shown in the GN8 book I think. Obviously there is a valid point that any joints need to be sound and ideally meaintance free but a properly implemented crimp (or solder) joint satisfies that aspect.

2 - add a 2nd rod which should bring down Ze to under the scams 200 ohm number. It will also mean there is a functional set of earth connections that are accessible
Definitely needed. While it might be getting TN values due to service pips just now, that could disappear if some plumber or utility replaces metal pipe with plastic pipe or push-fit joints.

3 - sort out all the damaged accessories, change the bathoom light, and maybe consolidate everything in one DB if customer agrees to extra cost
4 - run a new 4mm radial sockets circuit to the dining room, so in future this can be extended to rewire the kitchen.
Both make sense.
5 - remove the single class 1 light fitting (even though it's earthed) and just quote BPG 4 and say while the lighting circuit should be earthed it's rcd protected and all fittings are plastic, so it's only a C3 according to BPG4. Maybe also offer a 'quinetics' lighting rewire.
Not so sure about that. The BGP#4 is really talking about pre-1966 cable work that never had a CPC, not new systems that are faulty in terms of open CPC.

Could you take a CPC from another circuit to that segment of the lights?

Do you know if they are all open (i.e. some monkey just did not believe in CPCs for lights) or are they linked but one connection point back to the supply is missing?
 
Not so sure about that. The BGP#4 is really talking about per-66 cable work that never had a CPC, not new systems that are faulty in terms of open CPC.
I should have said - it is pre 66 cables. It’s not lack of continuity of cpc as coded, there is no CPC. Some switch drops have cpc but no fitting that I looked at.
Not greatest photo!


1660894166817.jpeg
 
I should have said - it is pre 66 cables. It’s not lack of continuity of cpc as coded, there is no CPC. Some switch drops have cpc but no fitting that I looked at.
OK in that case RCD and no metal accessories is fine.

Metal screws are OK as though technically touchable, they are not easy to do so and the regs do have some statement about that being OK.

EDIT: 410.3.9 (iii)
 
Thanks @pc1966. I’m encouraging a lighting rewire anyway.
There were two light fittings that experience has taught me not to touch unless I was ready to replace….!
 

Attachments

  • 89F7A0A1-A3B1-4110-9B36-56F972DBAC34.jpeg
    89F7A0A1-A3B1-4110-9B36-56F972DBAC34.jpeg
    391.6 KB · Views: 12
  • 6D460291-707D-45B1-B5B1-6ACAC3F7EBD2.jpeg
    6D460291-707D-45B1-B5B1-6ACAC3F7EBD2.jpeg
    320.2 KB · Views: 12
Thanks @pc1966. I’m encouraging a lighting rewire anyway.
There were two light fittings that experience has taught me not to touch unless I was ready to replace….!
The painted over one is going to be a joy to open :(

The brown one might be fairly new but "old style" as I have seen brown/gold like cables used in the recent part for vintage style lights.

But really they could both do with being replaced by new pendants and so on.
 
Is that a PILC incoming cable?

Looks from the picture like it may once have been TN-S there. That should really be bonded (or changed to TN-S) if there is an extraneous conductive part accessible. I’ve used this argument with U.K. Power Networks a few times when in a very similar situation and they’ve always provided a TN-S derived earth.
 
Is that a PILC incoming cable?

Looks from the picture like it may once have been TN-S there. That should really be bonded (or changed to TN-S) if there is an extraneous conductive part accessible. I’ve used this argument with U.K. Power Networks a few times when in a very similar situation and they’ve always provided a TN-S derived earth.
Thanks. @davesparks mentioned this too. I'm currently having this discussion with them. It isn't a priority call-out from their p.o.v
Picture sent to them and the lead sheath gives a low Ra.
I like the extraneous argument, I hadn't thought of that.
 