I was reading a thread on a different forum about someone asking how to wire the above, he was going to put the incoming into the top contacts and the outgoing into the bottom contacts leaving the middle pole free. I thought well that sounds fine but it reminded me of how I've seen them wired in the past where someone has looped the neutral back through the middle pole.

If I'm wiring them on single phase I usually unscrew and disgard the neutral pole that is usually attached to the side of the switch body and just do as above, what advantage is there in loopin the neutral through the middle pole, makes no sense to me. Its not as if its an expensive component and this extends the life in some way, they are cheap as chips.
 
This week we came across one where the line had been connected to the top and looped back through the middle. Neutral was through the bottom contact. It caused us a bit of head scratching as the center contact had failed open circuit.
 
There's no logic to looping it back through another pole in that scenario.
It may be a misunderstanding and just copying what you would do on a DOL starter.

If it were a DC circuit and both poles were looped back through on a four pole switch or circuit breaker it would increase the breaking capacity.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
North West
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
3/4 pole rotary isolator on single phase.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
oscar21,
Last reply from
Brother Blue,
Replies
2
Views
72

Advert

Back
Top