EastAnglian

Hi guys ..... I'm struggling through the project part of 2391-20. I took and passed the exam last June but getting the project complete is a nightmare!

Anyway, quite a long way outside my personal experience, is the initial layout of a 3 phase service to a building. The basic design is for a medium-sized public building and I'm looking at a 400A 3 phase supply. There will be 4 DBs in the building plus 2 3 phase delivery points for HVAC and Lift Gear.

Question is .... would it be normal practice to distribute the 3 phases to each of the DBs, and then share the final circuits across the 3 phases, or would you use a single phase to supply each DB? In my design DB1 and DB2 have a similar demand and DB3 + DB4 would come in at about 60% of DB1 or 2.

3 phase DBs at each point would of course result in separate phases being used in the same parts of the building, and 400V being present between parts of the light switch cluster for example.

Hmmm ...... nice little domestic jobs on a 60A service head do have their upsides!

Ta

Malcolm

PS .... please bear in mind this is a paper design exercise only
 
A number of factors would determine whether i would put in TP DBs rather than SP, primarily the need for any TP services off these DBs. TP Dbs do have a little more flexibility if the demands change over time and in your design you can still deal with loading balances and you can keep 400V popping up in switch boxes to a minimum by using the same phase in the TP DB for that particular application.
I would be initially looking at your overall demand calcs and making sure the 400A supply gets nicely distributed to give you the maximum flexibility for the future. So how will the 400A supply be terminated before it goes onto the Dbs, on a MDB ?
 
Hi P&S! Indeed, good sound advice. Yep, an MDB in the service room is the plan.

I keep forgetting its only an academic project ..... I get carried away with the idea I've got t source the parts and get then installed ;-)

Malcolm
 
Have you been given the individual loads supplied by this system? If the loads can be balanced (within reason) between 4 single pole boards then that is the way to go, if not then 3ph&n boards need to be used. It’s down to you to sort out the loadings.
A down side of single pole boards would be future expansion of 3ph loads.
Sorry the balls in your court.

[EDIT] just thinking about it a 400A incoming is pretty hefty so if your feeding SP boards then there’s some heavy cable involved. The lift is not likely to be much, the A/C unit you’ll have to check on. For the sub distribution I would go for TP boards. Makes the cabling more manageable. You also have to take in to account terminating the cables in a SP board.
 
Last edited by a moderator:
Thanks Tony ..... from tonight's calculations I can confirm that the size of the sub-mains do in practice determine the architecture, and it will be separate TP boards.

The individual loads are down to my design so I do have the data which enables the three phases to be balanced within reason.
 
Last edited by a moderator:
Thanks Tony ..... from tonight's calculations I can confirm that the size of the sub-mains do in practice determine the architecture, and it will be separate TP boards.

The individual loads are down to my design so I do have the data which enables the three phases to be balanced within reason.

Sounds about right in practice, i would expect the MDB to have say 4 X 125A breakers, feeding 4X TP boards with 125A incomers, run lift and HVAC off the nearest board, jobs a good un - oops assume all boards equally loaded and equal requirements for spare capacity.
 
Last edited:
i would say 3 phase sub-boards

can't think of any good reason to run single phase dist circuits and boards at all
 