R
richardhammond
hi all
just to confirm my knowledge (or to throw it in the bin)
a 3 phase adaptor running from a standard PAT tester should be wired as below....
incoming (3 Pin Plug) cpc connected to cpc on 3 phase socket
incoming (3 Pin Plug) neutral connected to neutral on 3 phase socket
incoming (3 Pin Plug) live connected to live on 3 phase socket (all 3 phases joined together)
So basically the 3 phase socket is wired the same as a normal socket with the exception that all 3 phases are connected together in the socket.
Re: 3 phase PAT adaptors
Well for starters - its most important that PAT adaptors for 3 phase equipt. do not allow a mains connection (inadvertantly or not) from the PAT testing equipment. So the first thing you do is snip off the "live" wire from the cable where you're going to terminate it into the adaptor. Next step connect earth (doh !!), then Neutral into first phase conection. Each subsequent phase is then looped together into the first. - see picture I've taken.
PAT testers are configured to apply insulation test voltage to both Live & Neutral, therfore it don't matter the "Live" is snipped off.
All of this is covered in Code of Practice page 76 Para 15.5 notes 4 & 5.
I set my Supernovas up to carry out this test and is listed separately on the test menu.​
Attached Thumbnails​
Read more: http://www.electriciansforums.net/pat-testing/31708-pat-testing-415v-equipment.html#ixzz1yq4I6zU7