Just had 3 phase installed to a house to be split into 3 flats. They have provided from 3 flat meters and 1 landlord meter a 100amp isolator to terminate my 3 core 16mm swa into. Do i need to now send that thru a 60amp fused isolator to each flat?
 
think he means 100amp isolator switch the answer is yes imo fit 60amp metal clad switch fuse that way can gland and earth armouring easily
 
Fuse in an isolator? Come on Sintra :flowers:

If it is a fused switch then yes down rate it. but I think you're going to end up with a bit of a silly situation of an isolator feeding a fused switch. Crazy but............
 
best thing for me to do guys is post u a pic of the final arangement provided by eon an we will go from there. lol all ur answers make sense. Check this space :) lol
 
tony understands exactly why am posting this lol so i need to see what eon provide first. At the moment i only have an 8x4 ply back panel with a 3 phase fused cut out on it lol. Need to wait and see wat the next monkey from eon will add past that hahah coz ive seen so many slightly different variation of the same job in the past.
 
Surely after the suppliers 3 phase cut out which i am assuming will be 3x100a BS88-3 there needs to be a 3P&N 100A isolator fed with a minimum of 25mm2 tails. From here a small 6 way ryefield should be placed (2x63A BS88-3) fuses per phase bar to allow sufficient space for the three flats and the landlords. You then can feed the 4 meters if they are to be communally positioned using 16mm tails and from there onto your armoured via a metal adaptable box enclosure or steel trunking to terminate your 4 swa cables. Label all up accordingly and job done. I am assuming all metering and protection is to be placed in a communal hall or equivalent seeing as the building is to be split into individual flats and landlords supply.
 
Thats how I expect it to become just waiting to see what the other switch gear eon r going to fit first :) cheers to all ur replys lads top site lol
 